Cooperation of PV farms with the transmission grid
Hello everyone,
I was searching for some practical information about PV farms but didnt get it. So I got few questions:
1. As we know inverter adjusts voltage to grid level (or transformer does it). What happen when voltage in the grid is lower or higher? Is grid sending signal about voltage level to plant and by this we can change the ratio of step-up/down voltage?
Which situation is better? When we got higher voltage in grid or lower than nominal?
2. What protection divices we use in PV farm? What about their settings?
For example we got fault in grid and farm got disconnected - should it back on its own to the grid after passing the fault? How it looks like?
What can you say about short circuit power generated by PV plants? As we know this power is needed to ensure stability of the grid.
Thank you for reading my threat and any activity. :)
RE: Cooperation of PV farms with the transmission grid
PV plants on transmission should ride through a fault.
Many PV plants will reconnect after a time, and after being knocked off.
Do PV plants actually contribute into a fault? My experience is not very much, and no negative sequence.
Either they should act like a rotating machine, or provide modeling information to utilities.
Most PV equipment manufacturers really don't care about grid stability. They are only interested in making money.
- If operated in unity or constant power factor mode, the inverter controls the magnitude of the voltage it generates on its side of the inductance. It matches the magnitude of the grid voltage it senses for unity pf output.
- If operated to produce a specific lagging or leading pf, it will produce a voltage magnitude that is lower than or higher than the grid voltage magnitude, respectively, to either consume or produce reactive power in proportion to its real power output.
- If operated to produce a specific reactive power, it will adjust its voltage magnitude with respect to the sensed grid voltage to do so.
2. Several protection functions are built into inverters to meet safety requirements per IEEE or IEC, but typically include over- and undervoltage, and over- and underfrequency, synchronization, anti-islanding, etc. However, external protection relays may be provided, and are sometimes required by the utility. Inverters will typically turn off their output when grid loss is detected after a period of time and will automatically resynchronize when the grid returns. Some inverters will inject/absorb reactive power during voltage sags/swells to aid the grid during such events with utility permission. Current output during faults is typiclly limited to be between 1.1 and 1.5 pu depending on inverter settings and capabilities.ERPI has a good report on inverter functions available here.
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
The protective devices employed on the farm side of the connection are dependent on the location within the facility, and what - exactly - you're trying to protect. Typical sensing should at minimum include over/under voltage, over/under current, ground fault, and phase unbalance on the facility side of the connection. On the grid side you can measure the same things, although you don't really have to. All you need to know is whether the grid is able to accept power or not, which is accomplished by fairly simplistic voltage and current sensing. If the PV facility gets disconnected (from a fault on either side of the connection), control logic should be in place to determine when both sides are ready to run again, and to make the reconnection.
The amount of short circuit power from a PV facility is going to be limited by the maximum momentary output of the converter(s) that change the DC generated by the panel(s) into AC for distribution. Typically, this is limited to 150 % of the continuous rating, and is only available for 60 seconds or so (followed by sufficient "dwell" time to allow the converter components to cool back down). In contrast, a rotating supply can easily handle 3 to 5x rated output for a similar duration. You may also be limited in how fast your system can respond to this kind of demand.
Overall, your electrical system is only going to be as good as the weakest link. That may be the utility lines, the transformer, the facility internal wiring, the converter, or even a single PV panel. It might even be the control logic. In some cases, it might be the geography and weather for the farm's location itself.
Converting energy to motion for more than half a century
Real power flow depends on the angular difference between the phasor voltages of the inverter and the grid across the output series inductance, not the magnitude difference. Reactive power flow depends on the magnitude difference.
xnuke
Since energy is conserved, I'm trying to understand this statement. How exactly does a PV farm motor? I'm imagining PV panels shining brightly into the night sky when the power flow reverses. Since this doesn't happen, I don't think PV farmers need to worry much about this "undesirable" effect.
Smaller installations likely do not receive a control signal from the grid, and instead just react based on the voltage at the point of interconnection. An example of how this works for modern inverters per UL1741SA is on page 20 of http://media3.ev-tv.me/UL-1741-Supplement-A_Webina.... Legacy inverters often had no ability to provide voltage support.
Solar plants at full output can cause high voltage on distribution lines. Although somewhat counterintuitive, solar plants actually often work to lower the distribution voltage during peak production.
The link I posted also mentions various kinds of protection required of modern inverters. This is still an evolving field, so there are different sets of requirements throughout the world.
stevenal If the converter doesn't have the correct protection, a power flow from the grid to the converter will definitely cause some disruption. The panels themselves might well survive, though. I live in a fairly rural area - it's amazing what some people think is an okay approach, when the preferred method to tackle any project is DIY.
For the greatest operational flexibility, utilities definitely prefer operating their grids as close to the maximum voltage limit as comfortably possible.
The Independent Electrical System Operator [IESO} in my province does not permit automatic reconnection of ANY generation at the transmission voltage level; IESO concurrence with reconnection must always be obtained first.
I also find this to be true; almost across the board, PV operators prefer to operate their plants in a manner that holds the reactive power flow on the low side of their grid connection transformers at unity power factor, passing absolutely no more current through their transformer's low-voltage winding than necessary, as this maximizes transformer life and minimizes equipment degradation; they usually care not a whit what happens to the system voltage as long as they can remain connected.
They usually only agree to undertake to either provide or absorb lagging reactive power to the grid if it's negotiated right into the operating agreement well before the first shovelful of dirt is ever turned to build the plant, in other words, only if there's money in it for them.
CR
Certainly! That's why residential grid-tie is all being forced to comply with UL1741 rules that include reducing output to prevent local distribution voltage rises. Some areas require a web connection to the utility so they can order your system off the grid. Some systems will not power up and supply anything to the grid until the utility's controller has authorized it. Witness the myriad Youtube videos of people who installed Tesla Power Walls only to discover they won't do anything until authorized by the utility's computer. In some cases the utilities don't even have a system in place to authorize operation so a powerwall is left useless for months. This can be really aggravating as during peak solar periods the utility can throttle back all the connected solar "to keep the voltage low" and then as soon as the solar availability drops off turn it all back up when no one has anything to offer. This can toast your ROI.
Keith Cress
I tried found some more information about it, mostly about how connections with grid looks like, but got only some articles.
Did you heard about it? Any inventer producer implemented that(i didnt find anything)? Are there also devices for PV farms not microinstallations?
The specific settings again depends on the results of the interconnection study/agreement.
For a utility scale PV, you will have external protective relaying. NERC PRC requirements direct protection/coordination/ride-through characteristics for utility scale PV, but typically a utility has their standards available for general protection expectations. This PV studies webinar is pretty useful to visualize what engineers are evaluating for various stages of utility scale PV developments.