On-off valve Hookup
On-off valve Hookup
(OP)
Dear members,
I have a XCV( fail open) and has to be slow opening , the idea is to demolish the old valve and install new one., but when I see the pneumatic hookup of the old valve, I don't understand it, I made a pneumatic drawing from the existing setup but could identify the clouded component and hence couldn't understand the working of the valve. can anyone help please?
Also please check the PDF doc in attatchment for additional info.
I have a XCV( fail open) and has to be slow opening , the idea is to demolish the old valve and install new one., but when I see the pneumatic hookup of the old valve, I don't understand it, I made a pneumatic drawing from the existing setup but could identify the clouded component and hence couldn't understand the working of the valve. can anyone help please?
Also please check the PDF doc in attatchment for additional info.

RE: On-off valve Hookup
Unless you've missed something in the drawing (like the solenoid valve being a 3-way valve instead of the 2-way valve that you have drawn), that "??" box has to be some kind of bleed valve for when air supply is shut off. There are no other bleeds shown on the system.
Have you cycled the valve and see where the air is discharged?
RE: On-off valve Hookup
In their you will find the small needle valve which controls the opening air flow and speed.
The second line is a little odd, but is either the vent line or they need two pipes to get the flow through the pipes to the actuator.
an actual picture of that box would help a LOT
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: On-off valve Hookup
RE: On-off valve Hookup
RE: On-off valve Hookup
You need to try and find the valve actuators diagrams in the P&ID legend sheet to figure this out.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: On-off valve Hookup
Those two protrusions in your first picture - the ones out the back of the box - look to be needle valves, presumably to control opening and closing rates. I stand by my original thought that this box regulates filling and bleeding of air pressure, but LI is right in his assessment that the arrangement makes no sense as it is piped unless the internals are more complex. As soon as the IA feed line solenoid valve (DI signal) shuts down, the whole system will be suspended at the IA supply pressure. The DI signal turning off the valve doesn't change the state of anything further downstream, so I'm not quite sure how this valve actually operated.
RE: On-off valve Hookup
I think there is an error in your flow diagram. The tee shown down-stream of your solenoid valve should be up-stream, although things may work the same as you have drawn things. The solenoid valve is probably actually a 3-way valve that exhausts air though a small port.
RE: On-off valve Hookup
The 5-way valve has only one pilot port so it must be spring return. And the solenoid valve must be 3-way or it serves no purpose.
RE: On-off valve Hookup
@ composite pro, Thanks for the reply,, the solenoid valve is indeed a 3/2 valve that controls the main air downstream as you see from the picture below.
Does 2 connections to the actuator necessarlily mean its a double acting type by default? or could one port be for the exhaust of the air?
I have numbered the ports , as I understand from the answers above, 5 and 6 are exhausts, while 3 is the pilot line? so in this case this valve is actuated by Air?? can we identify others ports as well?
RE: On-off valve Hookup
The actual P&ID shows a single acting spring return actuator opening slowly in case of failure, and in reality a simulation with a double acting actuator was installed.
Appears the failure case is no signal on the 3/2 solenoid. In case of failure the instrument air is no longer available and the instrument line to the 5/2 valve is open to the atmosphere due to the 3/2 solenoid. The 5/2 valve switches putting pressure on other side of the actuator, but now from the accumulators. The air on the other side of the accumulator will be free to the atmosphere through the 5/2 valve. In one the outlets of the 5/2 valve there will be an orifice ring to achieve slow opening.
RE: On-off valve Hookup
I assume what happens is that when the DI signal is energised, the 5 port block sees air pressure on port 3 which connects ports 1 & 2 to port 4, which is your air supply.
The valve opens slowly based on possibly some adjustment in that block. I think those two hose are both connected to allow enough air to flow in and out against the spring. The valve then stays held open by the air pressure.
Then to close the DI de energises, the section from port 3 and the non return valve depressurises via the DI vent, the block then switches between port 4 to port 5/6 and the valve starts to close as the air vents to atmosphere and the spring closes the valve.
You don't say anything about how fast the valve closes compared to opening. It may be the closing speed needs two hoses to get the air out of the actuator in 10 seconds? 15? It looks a fairly big actuator.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: On-off valve Hookup
Suggestion:
When the 5/2 valve is actuated, instrument air will flow from port 4 to port 1 or 2, or even both. The actuator will close the valve.
When the DI signal falls away, the upper IA system becomes atmospheric. The 5/2 valve switches in position. Now the accumulators air takes over. Most likely port 4 will than be connected to one of the ports 1 or 2, supplying air to the actuator through one of the lines. The other line connected from actuator to the 5/2 valve will be release air through port 5, 6 or even both. Could be that an orifice is mounted in the connector(s). The accumulators make the quantity of air to be released larger giving a slow closing valve operation.
RE: On-off valve Hookup
They normally have nothing to do with valve closure due to spring return action on the piston.
I still struggle getting a grasp of what this system looks like and am using the drawings.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: On-off valve Hookup
The accumulator must be there to move the valve to the desired position in case of air failure, and the valve will stay in that position until air pressure is restored.
RE: On-off valve Hookup
It's all a bit of a mess without clear knowledge of the box.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: On-off valve Hookup
In the new situation., The flow reducer valve needed in this case to reduce the opening time would be mounted on the solenoid valve exhaust port? does anyone have a drawing with any FO valves with such a setup? maybe there is a special spool valve to do this job?
RE: On-off valve Hookup
It makes no difference to the actuator if the valve is FO or FC - the spring moves the actuator the same - you just need to position the actuator 180 degrees different.
Don't be too hasty about removing the accumulators. They were there for a reason, which is if your air supply drops below min actuator pressure, your FO valve will start to open a little bit as the spring force overcomes the force from the air supply. Unless you n=know for certain that that doesn't ever happen, then the accumulators might be a good idea. Also if your valve is a long way from the air receiver, it might take a long time to close the valve if the air supply pressure drops due to high frictional losses.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: On-off valve Hookup
RE: On-off valve Hookup
RE: On-off valve Hookup
we decided to change the valve to a single acting as per the PID( dont know why it was double acting in the past) , and decided to hook it up as shown below. strangely, the client doesn't know why there was a accumulator vessel.!! and why it has to be slow opening( we did a new water hammer calc and turned out to be fine!)
hence decided to connect the old accumulator back and include a vent throttle valve to control the valve opening time if needed in future.