Kindly advise on Pre-Action System
sv879
AE
Dear Experts,
The diagram below depicts the proposed single interlock pre-action (+dry pendent, as directed by project consultant) for a cold storage area.
The detection portion is handled by the VESDA system. (The pre-action system does not have a control panel)
Kindly take a look at the scheme and give me your valuable feedback and suggestions.
Thanks in advance.
You'll need a panel listed for releasing to serve the preaction valve.
Instead of dedicated control panel / releasing panel for pre action, solenoid activation via fire alarm system control panel along with a normally open relay module proposed.
Kindly follow the below sketch for better understanding.
If you are in a jurisdiction using NFPA standards, the control unit for the preaction valve must be listed for releasing service. See NFPA 72 §22.11