Kindly advise on Pre-Action System

Status
Not open for further replies.

sv879

Mechanical
Joined
Dec 7, 2018
Messages
68
Location
AE
Dear Experts,

The diagram below depicts the proposed single interlock pre-action (+dry pendent, as directed by project consultant) for a cold storage area.
The detection portion is handled by the VESDA system. (The pre-action system does not have a control panel)

Scheme_fpg9wa.png

Kindly take a look at the scheme and give me your valuable feedback and suggestions.

Thanks in advance.
 
You'll need a panel listed for releasing to serve the preaction valve.
 
Instead of dedicated control panel / releasing panel for pre action, solenoid activation via fire alarm system control panel along with a normally open relay module proposed.
 

Kindly follow the below sketch for better understanding.
Pre-action_fdxxys.png
 
If you are in a jurisdiction using NFPA standards, the control unit for the preaction valve must be listed for releasing service. See NFPA 72 §22.11
 