Hi all, I am looking for some insight on the following situation.

I am designing a small one story addition onto an existing building. The addition is about 150 sf, and it is being detailed independently from the existing structure. Thus, it will have its own lateral system. My question is with regards to minimum wind loading. If the addition is detailed with expansion joints adjacent to the existing building edges, there won't be a net windward and leeward wind pressure applied to the addition. For instance, depending on the wind direction, only windward load or leeward load would be applied to the structure. Now, if those individual pressures do not add up to the minimum 16 psf, would I then technically have to design the addition for 16 psf of load rather than something far less in magnitude? This is a grey area in the code, and I would appreciate any feedback you may have.
Replies continue below

Recommended for you

RE: Minimum Wind Load

Good question. Hadn't really thought about that before. I'd probably start with the full 16psf and see how crazy the design gets. If it's not too bad, then stick with it. If you can't make it work (or it only work if you put in a steel brace or something equally ludicrous for a 150sf addition) then back off a little.

I'd probably look at your various load cases and apply the 16psf in each case in a manner proportional to the windward and leeward pressures you calculated. For example:

Case 1:
Windward Pressure = 9psf
Leeward Pressure = -3psf
Total Effective Wind Pressure: 12psf

Windward is 9/12=0.75, so apply a windward pressure of 16*0.75=12psf

Of course this gets more complicated with taller buildings or buildings with multiple diaphragm heights where you need to divide it up a bit more based on actual elevation pressures. But this should start you in a reasonable direction.


Thanks for correcting me, MotorCity. I was thinking there was a statement about a combination of windward and leeward in the code. That's the implication (it only matters if windward+leeward is less than an effective 16psf), but it's not written that way.

I disagree on the shielding comment in this case. Shielding is meant to apply to other buildings and terrain features. There is no 'other building' in this case. It's a 150sf addition. That tells me it's probably a utility room or a small sun room. Maybe a bedroom? It's part of the other structure. If it were separated by a short breezeway or set 5' away, then sure - no shielding. But if it's built by cutting a door opening in the wall of the existing building and building three walls to enclose the space, it's an addition and part of the the existing regardless of how you want to resolve the loads. Checking to make sure a 3-sided diaphragm works in that situation is a matter of expediency that is usually acceptable in small residential or other RC II structures at strength level design (which is where the 16psf comes into play). Have to be a little more careful with serviceability since you can could get some unintended load transfer.

If they went through the trouble of detailing the connections, the OP would be justified in analyzing the entire structure - existing and the addition - as a whole. That effectively means that the the existing structure would 'shield' the addition in one direction.

Of course we haven't seen a plan and we haven't been read in on the construction type, so maybe I'm not being conservative enough in light of the lack of information.

RE: Minimum Wind Load

The minimum 16 psf wind load is just that....a minimum, whether its windward, leeward, or a combination of both, a minimum load of 16 psf needs to be applied to the structure. It sounds like this is a horizontal addition to the building and you are looking to use a smaller wind load due to it being shielded by the existing building. Unfortunately, you are not permitted to consider shielding.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close