Gerre,
You seem to be talking about something called a "frangible roof design" (FRD) which is mentioned in API-650 and several other references.
Yes, failure of the roof to shell joint becomes important under fire or emergency conditions. ...But there is a lot more to the story
There have been several threads on the Storage Tank forum and other places dealing with this type of design.
Some things you should know are:
- As per API-650, its not suitable for smaller diameter tanks (What is the diameter of your tank and what, specifically is being stored ?
- Robust tank anchorage design and bolt sizing is also very important
- FRD is an older method of shell protection; Insurance companies like to see properly sized emergency vents on the tank
- FRD is also discussed in Storage Tank Design Code EN 14015; Appendix K,
Research Article here:
Also see this discussion:
Give us more details about your particular tank design ... Can you post a drawing or sketch ?
Are you a new hire and is this the first storage tank that you have been assigned ?
What is the Code of Record for this tank ?... Where will the tank be located ?
I have never heard of this design called a "fish mouth"
MJCronin
Sr. Process Engineer