Greetings,
As per ASCE7-10 section28.4.4 , the minimum design wind load shall be 0.77 kN/m2 for wall and 0.38 KN/m2 for slab , my question, is the value of P=q *( GCpf - GCpi) shall calculate for each each wind exposed element ( leeward, windward , end zones , side pressure,…….etc) and then compare with the min. Values above and take the max.
For sure there are many values will be lesser than the above min. Values , because of this i feel there is another condition to use the above min. values, please see snap below and advise.
Thank you
Thank you