hello, what does two-stack type switchgear means?

RE: Medium Voltage Switchgear

Two breakers, one above the other, in a single cubicle of gear.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Medium Voltage Switchgear

(OP)
Hello, davidbeach do you have brands which use the two-stack type?
Was it ANSI or IEC?

RE: Medium Voltage Switchgear

All ANSI, but every line of switchgear I’ve looked at includes stacks as well as singles. No idea about life in the IEC world.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

RE: Medium Voltage Switchgear

Hi, It implies that breakers are arranged in 2 tier fashion, 2 breakers in a vertical section.

RE: Medium Voltage Switchgear

Dear Mr. PoliPoliCarps 8 Jul 21 02:35
" hello, what does two-stack type switchgear means?
do you have brands which use the two-stack type?
Was it ANSI or IEC?
"

1. If you look into any manufacturer LV switchgear catalogues, you will see what is "two-stack" as explained. For LV switchgear there are even "three-stack".
2. For MV due to bigger physical size up to say 22kV with vacuum or SF6 breakers, there are "two-stack" design available on the market.
3. This is applicable to IEC or ANSI world.
Che Kuan Yau (Singapore)

RE: Medium Voltage Switchgear

Low voltage is 4, medium voltage is 2. Low voltage is almost always 4, but for MV, industrial/commercial customers almost always go 2 but utility customers often limit it to one per section.

I’ll see your silver lining and raise you two black clouds. - Protection Operations

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close