Motor contactor wiring check
Motor contactor wiring check
(OP)
I am currently in the middle of learning electrical circuits for a project so go easy on me. I am wanting to make sure how I have our motor contactor laid out is correct and safe. If not, where can I improve?
Top L is incoming supply, 220V single phase that routes through a circuit breaker.
Circuit will have a STOP, START, and an Indicator Lamp.
Bottom R is outgoing voltage to a Servo motor drive with fusing before the drive.
CB and Fuse locations are specified in the servo drive manual.
No wire numbers yet, just indicating colors; Black (L1), White (Neutral)
Top L is incoming supply, 220V single phase that routes through a circuit breaker.
Circuit will have a STOP, START, and an Indicator Lamp.
Bottom R is outgoing voltage to a Servo motor drive with fusing before the drive.
CB and Fuse locations are specified in the servo drive manual.
No wire numbers yet, just indicating colors; Black (L1), White (Neutral)
RE: Motor contactor wiring check
Wire numbers would help. You need a black wire.
Well, you nave wires connecting the "Emergency Stop Button", the "Power on Button" and the pilot light.
From that common point, run another wire to T3. (In place of an auxiliary contact.)
Run a jumper from L3 to A1.
Disclaimer:
This advice is based on the components being as described by the standard symbols.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
First off you do not use the same 220 V to feed the servo as you use for the control circuit, they need to be separate with there own fuses.
Start with that and come back.
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
On a small motor, the circuit breaker may provide acceptable protection for short control circuits.
Different codes, Red.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
The CB and fusing is from the manual, size and placement.
RE: Motor contactor wiring check
Coming from the industri world we would never make a stand alone funktion like that, so we always separats everything like power and control circuits.
With our standards that would not be a correct emergency stop function either.
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
If it is powered 220 V AC it would have sade L1 ,N at least in Europe.
BR A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
RE: Motor contactor wiring check
So one needs to read the manual properly to get it right, if the servo is programable there might be settings that needs to be made.
BR A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
Don't feel bad. I found out the difference just in time when hooking up a European standby generator to a North American system.
The consequences could have been more exciting than finding out in a friendly discussion.
MScarn: I gave you a circuit based on the standard three wire motor control circuit that was old 60 years ago, and based on this disclaimer: Now you add non-standard information.
Check the manual, or RTFI.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
RE: Motor contactor wiring check
European standard L1 N = 220 VAC L1 L2 = 380 VAC and R, S, T incoming, U, V, W outgoing
I just saw 220 VAC and thought yes
I am very much for reading manuals so I guess I would have figured it out, if I had to.
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
In the 40's the standard voltages in North America were 110/220 Volts. In the 50's the voltages were raised at the rate of 1/2 Volts per year until 120/240 Volts was reached.
We had 5 years at 112/224 Volts, 5 years at 115/230 Volts, 5 years at 117/234 Volts and finally 120/240 Volts.
After generations of 110/220 Volts, the non-electrical public continued to refer to 220 Volts. This has been passed down to people who were born after 240 became the standard.
To make matters more confused, we see a lot of imported Asian equipment for the North American market labelled for 220 Volts.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
Edit; I see I have a wire color mislabeled @ L1 (should be black, not white)
RE: Motor contactor wiring check
I still think about European standard as 220 VAC, 3-phase 380 VAC but now it is actually 230 VAC, 3-phase 400V.
I am getting old.
/A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
What does the manual say?
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
Signals like enable, inhibit, backward, forward and run.
If this signals are going to be used the control power must be intact even if the power feed is off.
Depending on the drive or the function of the motor it can sometimes become a problem cutting off the control power since this functions can't be utilized.
But not knowing the servos functions or the motors function it is hard to tell.
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
Why are you wanting a contactor ahead of a servo drive? Are you aware that it's not really a good idea to control a servo drive by turning power on and off to it every time? Servo drives, like all electronic drives, have what's called a "pre-charge" circuit inside that prevents the DC bus capacitors from damaging themselves when you first apply power. The pre-charge circuit puts a current limiting resistor in series with the DC feed to the caps for a second whenever you apply power, then shorts around it with a relay contact once the caps are fully charged. That resistor and relay have a limited lifespan, usually about 1,000 operations. So if used once in a blue moon, you may never see it fail in your lifetime. But if you cycle power once per day, you consume that lifespan in <3 years, if you do it 10 times per day, <1 year! As a general rule, having a "safety contactor" ahead of it is fine, because ostensibly that is only going to be operated in an emergency. But if thus is for general on-off control (meaning the "Panel Power On" button you show), I would feed that to the servo drive directly, leave the contactor tied only to the E-Stop only.
Your control circuit is incorrect by the way. The Power On pilot light will glow ever WITHOUT the Panel Power On button being depressed and the Aux contact (L3/T3) is not going to seal in around the Power On button. The way you have it will seal in around the E-Stop!
I'm also curious as to why your Servo drive has an L!, L2 input and an R,S,T input? I'm thinking these are the SAME input points, just labeled for different parts of the world; L1, L2 for North America where it would be more common to have 240V single phase, and R, S, T for the rest of the world where 240V 3 phase would be more common. A simple check would be to see if L1 and R are common to each other.
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: Motor contactor wiring check
Connections at the servo; L1 and L2 are the control circuit, R and S is for single phase Main power.
RE: Motor contactor wiring check
RE: Motor contactor wiring check
RE: Motor contactor wiring check
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: Motor contactor wiring check
The wire to the auxiliary contacts should come from the jumper between the stop and the start buttons.
Good catch on the pilot light.Jeff. The pilot light wire should be from the other side of the start button.
With the original wiring the pilot light would indicate "Mains Present" NOT "Drive Power Energized".
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
Is it correct that if I had 3 phase power and L3/T3 were taken, then I would need an add on auxiliary contact?
RE: Motor contactor wiring check
RE: Motor contactor wiring check
I guess the start button is resilient and that you are going to use the emergency stop as a stop button too?
In the last example, one problem I have is that the you have constant power on T3.
Usually both for safety reasons and when measuring when looking for faults you expect all incoming power feeds to be on the same side of a contactor or relay.
L1, L2, L3 or T1, T2 ,T3 in your example it is L1, L2, T3.
In the picture above.
The black part to T3 and the black part to the lamp, should be connected on the left side of the start button.
And the part between A1 and L3 must go away.
And then you have to have a part from the left side of the emergency button to L3 instead.
I am a bit
BR A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
Only the lamp wire needs to be moved to the left of the start button.
No other changes, except.
Optionally the connections to L3 and T3 may be interchanged. The circuit will work the same but that will agree with the convention that constant power is on the top and switched power is on the bottom.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
I still think this would be a "nice" solution.
Or am I still to
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
Power contactor off: coil deenergized > lamp off
Start button pushed > coil energized > contactor pulled > lamp on
Power contactor on: Start button released > coil energized over L3-T3 > contactor pulled > lamp on
Power contactor off: Energency button pushed > coil deenergized > contactor fallen > lamp off
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
The connection from the start button to T3 should go from T3 to A1.
Electrically equivalent.
BUT:
The length of wire; T3 to A1 is a few inches. Start to T3 may be a couple of inches or it may be considerably longer.
When I taught a hands on course on industrial controls to industrial electricians, part of the course was an awareness of how a seemingly insignificant change in the wiring diagram could affect the amount of wire needed. Consider a conveyor with a stop-start station at each end. Do you want to run three wires for the length of the conveyor or run four wires?
The other issue is terminal points. we try to run from terminal to terminal and avoid splicing of more than two wires.
The terminals on most control devices will accommodate two wires.
The pilot light is normally located with the push buttons. It is normally the second wire connected to the left side of the start button.
With the T3 wire connected to A1, no three way splices are needed and no terminal has more than two wires.
PS: I like the way that you have interchanged L3 and T3.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
Waross, I see your point about the using the wire runs efficiently, and avoiding the 3 wire junction. T3>A1 solves both.
RE: Motor contactor wiring check
Best Regards A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
You mean you prefer it like this.
Or maybe even like this
Or maybe this is better
/A
RE: Motor contactor wiring check
When I was heavily involved in both teaching and on the job control circuits, all of the major North American control manufacturers published booklets of standard motor control diagrams.
I tried always to base my circuits on standard circuits.
This had an advantage of making trouble shooting much easier for less experienced electricians.
I remember working on a printing press with both AC and DC motors some of which were reversing.
It took a while.
The drawings were in a non standard (By North American usage) format, and...
The prints were in Italian.
It was a long afternoon.
My boss had started on the press.
He was an excellent trouble shooter.
When he called me for help I knew it was going to interesting and challenging.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
RE: Motor contactor wiring check
We also have an Italien Press where someone hade managed to reorganize the ElCad project, so all the contacts for contactors and relays hade been moved around in number order.
Witch meant that there it should have been a NO it could be a NC.
Looking in the drawing i was not possible to reset the emergency stopp.
It took years to fix the drawing so it became as it should and it was in Italian, Frizioni Motori
/A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein
RE: Motor contactor wiring check
/A
“Logic will get you from A to Z; imagination will get you everywhere.“
Albert Einstein