4 speed wiring configuration
2

4 speed wiring configuration

4 speed wiring configuration

(OP)
I have an old master electric company motor I'm looking for information on wiring configuration for the different speeds. It's 480 volt 4 speeds I believe it has 14 leads plus 2 extra wires I believe those are a thermal device. Leads are labeled 1 threw 7 and 11 threw 17. I have attached the name plate of the motor. Any help would be great!

RE: 4 speed wiring configuration

Would be interesting to know how they achieved same 10 HP from 1750 RPM all the way down to 575 RPM.

Muthu
www.edison.co.in

RE: 4 speed wiring configuration

I am guessing an oversized frame and two, two speed windings.
I suspect that the HP is limited by the winding ampacity and not by the frame capability.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: 4 speed wiring configuration


Mjgjovik
Probably, there are two Dahlander windings.
Need some additional info.
Contact us for more details.

ACW

RE: 4 speed wiring configuration

I confirmed with EASA that it is indeed double Dahlander winding. Master was apparently early avatar of Reliance Electric.

I suggest you take the motor to a good repair shop to test and tag the winding leads and to make connections schematic for the 4 speeds.

Muthu
www.edison.co.in

RE: 4 speed wiring configuration

I once spent an afternoon identifying the unmarked leads of a Dahlander motor.
Tools, a multi-meter, a truck battery and a compass.
I took resistance and continuity readings, as well as voltage drop readings with the battery across connected windings.
I pulled the rotor and checked the physical location of the windings with the compass.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: 4 speed wiring configuration

Quote:

I once spent an afternoon identifying the unmarked leads of a Dahlander motor

And this is a double Dahlander!

Keith Cress
kcress - http://www.flaminsystems.com

RE: 4 speed wiring configuration


It is very likely the data from the nameplate are sufficient to reconstruct the external wiring for each speed separately, if the winding is made in accordance with this data, which is not always the case (intentionally or unintentionally).

Internal connections and external wiring

RE: 4 speed wiring configuration

Each Dahlander winding will have normally six leads out. Measure the DC resistance of all six leads with micro ohmmeter. 3 leads will read 50% higher resistance (e.g. 15 mohms) than the other 3 leads (e.g. 10 mohms). The ones with higher resistance are for high speed and the other 3 with lower resistance are for low speed. How they are connected is shown below. Delta is low speed and Double Wye is high speed. The rotation direction should be checked after reassembly and before coupling to load to ensure same rotation direction at both speeds. For each Dahlander in a double Dahlander. 3eyes



In double Dahlander winding, it it most likely one delta corner in each winding is opened to prevent circulating currents and hence the 14 leads the OP has posted. And it complicates the connections since the open corner has to be reconnected for that Dahlander while the keeping the corner of the other Dahlander winding open. Bummer. evil

Muthu
www.edison.co.in

RE: 4 speed wiring configuration

Here's what I have for a Constant Horsepower 4 speed motor. (Horsepower is the same at all speeds as denoted by the OP's nameplate photo.)
The path between T1 and T11 is permanent... and likely a internal connection... but not certain.



John

RE: 4 speed wiring configuration

You said it better, John.

What does L2 to C mean?

There is always focus on how a wye/delta starter is harmful for the shaft, motor etc. Wonder if anyone did 'transition stress' studies for this multispeed monster. glasses

An acknowledgement from OP for all the excellent free advice here would be nice.

Muthu
www.edison.co.in

RE: 4 speed wiring configuration

Edison, I'm not certain what the meaning of the "C" in the L2 column indicates.
It's from Westinghouse multi-speed drum controller information and may pertain to something about the switch.

The diagram I have for the constant torque connection shows the "C" in the L1 column.

The supplied schematic at least gives the OP enough to go on in making experimental connections
to get the beast-of-a-machine running.

John

RE: 4 speed wiring configuration

The controller for that motor needs a "4-on-the-floor" lever:

RE: 4 speed wiring configuration

Thanks John. Drum controllers? Long time, no see.

Also, wondering why would they start with high speeds and then go down to low speeds. Going from low to high speed makes more sense.

I have asked EASA about L2 to C. Will come back with their response.

Muthu
www.edison.co.in

RE: 4 speed wiring configuration

The earlier posted diagram is from information published in 1956.

Here is the same information published decades later in 1999.
(I always go to my oldest sources first, and work up from there ; )

Note that highest numbered labeled leads are the high speed.

Spar, your four-on-the-floor reminds me of how I may have to reach for the fifth under the seat after this post.

Getting back to work,

John ; )



RE: 4 speed wiring configuration

It's been a long time, and I have misplaced some of my books during my joirneys, so someone else may confirm this:
I remember variable torque constant torque and constant HP.
I seem to remember that, depending on the type of motor, while the connections are the same, the speeds may not be the same.
Depending on how the winding polarities are arranged internally, the consequent poles (low speed) may be formed with the windings either in series or in parallel.
With that in mind, the drum switch connections may be slowest to fastest.

A related question:
Given that there are at least two possible consequent pole connections, does Dahlander refer to any consequent pole connection or to only one particular connection?

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: 4 speed wiring configuration

What an educational and instructive thread!

I've never had anything to do with a Dahlander motor, and thus didn't previously follow threads mentioning them due to lack of interest, but I've learned a lot from this one.

So [ based on the pic of the nameplate ] the set-up allows for the motor to operate as an induction motor having either two, three, four or six sets of poles, depending on connection; neat! And reversible to boot!

Even if the OP did do a post and ghost, I sincerely thank you.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: 4 speed wiring configuration

All of the above applies if there are two Dahlander windings 12/6 and 8/4 poles), which is very likely given that the motor is old.
But it should be noticed that another variant is possible, i.e. two PAM windings (12/8 and 6/4 poles).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close