Reverse kVar protection of genset

Reverse kVar protection of genset

(OP)
Hi,

May I seek some advices about the reverse kVar protection: is diesel genset normally equipped with reverse kVar protection?

RE: Reverse kVar protection of genset

More info needed. IS the diesel connected in parallel with power grid or other generators?

RE: Reverse kVar protection of genset

In a paralleled set, the VAR production and direction of a individual set is controlled by the voltage setting of the AVR.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Reverse kVar protection of genset

You might do some searching on "loss of field" protection and "generator capability curves".

RE: Reverse kVar protection of genset

Generator doesn't take-in VArs unless there is problem with its excitation.
Hence, Reverse kVAr protection can be called Loss of excitation or field failure protection in other words.
But, reverse kVAr is possible only when there is kVAr source external to the generator - power grid or a transformer incomer paralleled at the same LV bus etc.

RE: Reverse kVar protection of genset

(OP)
@ thermionic1

We have 2 cases: 1. single genset not connecting to grid any time. 2. multiple parallel gensets, also not connecting to grid any time.

Thanks

RE: Reverse kVar protection of genset

Reverse VARs are the result of under excitation.
With a single set, under excitation results in under voltage.
With a paralleled set, under excitation results in reverse VARs.
See dpc's post. "Loss of field" or "under excitation" protection.

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Reverse kVar protection of genset

Quote (RRaghunath)

Generator doesn't take-in VArs unless there is problem with its excitation.
In my experience that does not hold for all cases.
Its entirely possible to have an islanded power station with at least one feeder providing VArs. Depending on the loading of the feeders and the overall station its possible to have an export of watts and import of VArs, although this is likely not a condition that would occur very often, perhaps one or two sites out of thirty three as a matter of perspective. If your intent is to detect a loss of excitation, noting that its possible for an import of VArs to occur under certain normal operating conditions then that is more accurate.

However, the value of the protection depends partly on what you're protecting and partly what you want to happen when a condition such as loss of excitation occurs. If we're dealing with supplying an islanded network with no other sources, then;
Single set, any reverse VAr protection must be set with consideration of whatever the VArs of the load need to be so that it only trips at a point where loss of excitation is likely. If excitation is lost or failing badly then undervoltage should also pick up.
Multiple sets, then the other sets will have to both supply VArs for the load and to excite the set with failed excitation. Voltage protection won't pick up as the other sets will keep the voltage in line, as per what waross has said. Depending on the characteristics of the load it may provide benefit, but not necessarily enough to look to implement it by itself if not fitted.

The case in point above, the station ran happily for a number of years without the reverse VAr protection on the sets, and no knowledge of the VAr loading of the feeders. New controllers were fitted, including reverse VAr protection, and a number of trips ensued before the settings were reviewed and it was discovered that under certain light loading conditions one of the feeders went capacitive.


EDMS Australia

RE: Reverse kVar protection of genset

(OP)
Thanks all for the valuable advices!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close