Designing a dention pond
Hi All;
I am designing a detention pond that will have no outflow - that means water will be detained till it evaporates. And of course I will design a primary spillway.
The pond will be concrete lined (or concrete canvas) and it will be in an aried environment - but when it rains it has a high intensity (25 yrs storm - 1 hour duration has an intensity of 60mm/hr)
I have the IDF curve for 2 - 5 - 10 - 25 - 100 year.
What is the used practice to size this pond - I mean is it 24 - 2 years storm as I read in some online documents or else ?
Appreciate very much your help
Best Regards
Ashraf
Best Regards
Ashraf
RE: Designing a dention pond
Peter Smart
HydroCAD Software
www.hydrocad.net
The owner is to find a solution for local stormwater management - and of course, for the owner, he is seeking the cheapiest accepted solution.
I found that a detention pond is the cheapiest solution.
Any comments ?
Peter Smart
HydroCAD Software
www.hydrocad.net
I needed to confirm what is the runoff to account for - some documents on the net specify 100 yr 2hrs storm - some 100 yr 24 hrs storm, and some (especially in parking lots)it is a 2 yrs 24 hrs storm
I will echo the above recommendations: design to the standards of the local agency with jurisdiction and provide a good means to deal with overflow.
--Winston S. Churchill
The site is in Saudi Arabia - North West coast and there is no mention to this point in the local standards at all. it is very hot in summer (around 45 C) and about 20-25 in winter aired environment - but when it rains it gets really bad.
The IDF curves sound unreasonable if I am going to calculate the runoff using the modified rational method - so I have to double check with reasonable requirements if I am going to use those IDF curves
Thats why I am bothering all my colleagues
IDF curves are normally used for estimating peak flow for short duration event and Depth-Duration-Frequency (DDF) tables are normally used for pond design, which must handle longer duration events. I have used the Modified Rational Method and IDF curves for pond design where there was no DDF data available, but that was a long time ago. Now it's easier, at least in California, to get good IDF and DDF data for the locations I deal with.
If you can find local DDF tables, that would be better than using the IDF curves. Your IDF curves end at 6 hrs and you need a longer duration for pond design. I don't like to extrapolate and using data for one to six hours and extrapolating out to two to ten days is not a good idea.
- and by the way: what do you mean by RCJ standards, I did not get what it refers to
In conclusion - I can see most of the design standards are specifying a 100 yrs storm - for at least 24 hours.
I tend to use this value - and it seams very rational.
Best Regards
Edit link to Ontario guidance
https://www.ontario.ca/document/stormwater-managem...
I found a refernce in the manuals of highways design (drainage part) from the ministry of transport