Eng-Tips is the largest forum for Engineering Professionals on the Internet.

Members share and learn making Eng-Tips Forums the best source of engineering information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Do you consider "breakout" when designing infiltrators for roof runoff?

Status
Not open for further replies.

meatymatt

Civil/Environmental
Joined
Apr 10, 2013
Messages
12
Location
US
Do you place geomembrane liner along storm trenches similar to septic? Working on a project where reviewer is "recommending".
 
Generally yes, with time th esoil around your rock fill will migrate into the voids and you will loose volume and hydraulic conductivity (assuming i understand this as a rock filled soakage trench for stormwater) likewise you need to try to prevent sediment cominginto the soakage system from the storm runoff - either pre-treatment, downturn on inlet pipe in manhole, perforated pipe with slots on the top half of the pipe only, means to flush out the perforated pipe etc)
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top