Dy11 TX not connected RYB to ABC
3

Dy11 TX not connected RYB to ABC

Dy11 TX not connected RYB to ABC

(OP)
Hi
We have a few situations where 11kV/400v TX's are put up poles that have their ABC terminals connected to BYR phases in that order so won't parallel with the next transformer down the line that has been put up the conventional way of connecting RYB to ABC. (The Tx's have been fitted up poles n opposite sides of poles) Does anyone have a quick method of drawing this out either with vector diagrams or simple analogies to explain why it won't parallel. Thanks

RE: Dy11 TX not connected RYB to ABC

Did you check vector diagram of voltages between two transformers? Can you show it?

RE: Dy11 TX not connected RYB to ABC

(OP)
Thanks Beyond86 - both Transformers are Dy11. I am waiting for the exact voltages between the Transformer secondaries but we do know they won't parallel. We have had this in other parts of the network and I just can't think of a way to prove it graphically why it won't parallel.

Thanks stevenal - I couldn't get the document to open here so will try it from home in case there is a block on opening files etc.
I have added a photo of a drawing showing what I was trying to describe, but just can't think of how to draw it out vectorially or some other way.


RE: Dy11 TX not connected RYB to ABC

Darn, engineering.com broke my link.

Update: I edited the first link so it now points to the same file now found elsewhere. The second link was to my own sketch illustrating the steps. You may be able to follow the steps without it. I used ABC for the conductor designations and H123, X0123 for the transformer bushings. Adjust as needed.

RE: Dy11 TX not connected RYB to ABC

Your displacement is off. There is a 60 degree difference. Roll R & B on one XF.

RE: Dy11 TX not connected RYB to ABC

The case you have mentioned is
1) RYB sequence to RYB terminals of Dyn11 transformer. This means standard phase seq is given to a transformer with standard polarity. Pl. refer to Fig a.
2) BYR sequence to RYB terminals of Dyn11 transformer. This means reverse phase seq is given to a transformer with standard polarity. Pl. refer to Fig d.
You will find a 120deg phase difference between a1a2, b1b2, c1c2.
https://res.cloudinary.com/engineering-com/image/upload/v1621049979/tips/IMG-5317_r2qkoy.pdf

RE: Dy11 TX not connected RYB to ABC

Forget about a to a, b to b, and c to c...
Think about rotation and displacement.
Let’s say RYB is ABC rotation. That is, B follows A, and C follows B.
You connect it to the XF with R to H1, (which I’m assuming you are calling A on the XF)
Y to H2, and B to H3. On your nameplate it will look exactly as shown with the secondary lagging the primary by 30 degrees.(or high side leading low side by 30 degrees)

Now, take the exact same transformer as you have done and connect it as you have. That is, R to H3, Y to H2, and B to H1. The nameplate drawing is now a “mirror” image. You are now “rotating” through the transformer backwards, which when drawn out shows you now have the secondary leading the primary by 30 degrees. (Or high side lagging the low side by 30 degrees) IA+ic=ia. IA=ia-ic

When you try to parallel these two transformers on the secondary side, (swap the a & c wires on one XF to try to match rotation), you will find there is a 60 degree difference in the voltages.

That’s where the 120 and 60 degree disagreement is coming from in these posts.

You can fix rotation on the secondary side by swapping wires to parallel. You have to swap wires on the primary side to fix displacement issues.

RE: Dy11 TX not connected RYB to ABC

(OP)
Thank you all very much.
Thats all great info, makes sense to me, I was struggling to work out how to show it. Much appreciated

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close