10x10 Timber Beam Sagging in century old home
4

10x10 Timber Beam Sagging in century old home

10x10 Timber Beam Sagging in century old home

(OP)
Hi all,

I am looking to find a viable solution to fix a cracked beam that is sagging. The issue is that there max 2 inch clearance between the beam and the furnace below, which is also the lowe point of the beam. see below



My proposed solution is to add 1/4" thick steel angle (i.e. lintel) below beam and support it at each end. The steel angle is the only thig I can think of to be able to slide between the beam and furnace, see below.



Any suggestions?

Thanks in advance.

RE: 10x10 Timber Beam Sagging in century old home

What is the connection detail of the floor joists to the beam? How do you "notch" the floor joists, to fit the angles, without detaching the joists from the 10 x 10 beam?
If you can put one new column on one side of the ductwork do you really need to install the angles? reducing the beam span may be enough to avoid "fixing" the beam.
If you can put one new column on one side, can you put a new column on each side of the ductwork and don't use the angles?

www.PeirceEngineering.com

RE: 10x10 Timber Beam Sagging in century old home

(OP)
The beam and the joist are notched, the joists run through the beam. Hope the image below clears it up.

RE: 10x10 Timber Beam Sagging in century old home

Two acrows?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: 10x10 Timber Beam Sagging in century old home

Looks to me like this is the old timber frame connection where a slot was cut partially into the main beam to provide the "beam hanger". The joists do not run through the beam.

Looks like crack in beam is located at the bottom of the notched end joist beam seat. Is the second photo of the opposite side of the beam? Crack looks smaller on that side, if so.

Think your idea of a steel post with saddle on either side is a good one. Is the floor slab thick enough to carry the post load. In a house that old, it might be pretty thin - depression era cheap?

Could do pier block with adjustable post (Simpson Strong Tie) and 6x6 post. Then you could jack upwards to take out sag.

RE: 10x10 Timber Beam Sagging in century old home

(OP)
@Sawbux
Really like your idea of pier block with adjustable post. The challenge will be fitting the steel angles under the beam, it might interfere with the joist.

Is it a bad idea to hire a contractor and remove the ductwork first? doing this will cost me a lot more but not sure if there is a way around it.

@PEinc
My concern is that the crack in the beam is too wide, and beam has sagged. if I jack it up and place post on either side of the furnace, I am afraid the beam might fail.

does this look like shrinkage crack? should I be alarmed? see close up picture below.




RE: 10x10 Timber Beam Sagging in century old home

Does the crack go all the way through? It could just be typical checking of old growth timber. But the sagging is potentially a bigger concern. And jacking it back up may cause more issues than it fixes. Jacking the beam could cause finish damage above the beam if the sagging has been in place for a while. If it is new sagging, then what has changed to cause it? Higher moisture content of the area? Change in loading? If it isn't new, then be sure the fix is absolutely necessary before going forward with it.

RE: 10x10 Timber Beam Sagging in century old home

Had a similar issue once, we used a channel flange down so that there was no notching needed.
We added two posts and then gradually tightened them over about 9 months. We never did get them jacked all of the way up, it became obvious that we didn't need it since it had always sagged some.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed

RE: 10x10 Timber Beam Sagging in century old home

(OP)

Quote (EdStainless)

Had a similar issue once, we used a channel flange down so that there was no notching needed.

I am having a hard time visualizing how you installed the channel flange and avoided running into the joists? Now my issue is that i don't have much room under the beam because of the furnace, prob 2 inches.

Quote (jayrod12 )

Does the crack go all the way through?

The crack doesn't go all the way through the beam but its fairly deep and wide.

Quote (jayrod12 )

If it is new sagging, then what has changed to cause it?

Its hard to say, I know next door to us they are building a 4 storey high condo, they had drill rigs for deep foundation, lots of shaking and vibration. Contractor excavated massive hole prob 30+ feet (underground parking). They placed shoring wall around and dewatering for months.

RE: 10x10 Timber Beam Sagging in century old home

If it were new sagging, you would likely have damaged finishes above this area, especially if it is brittle finishes like drywall and plaster. If nothing new has surfaced in terms of finish damage, then it's quite possible that the sagging is existing.

Now, even if the sagging is existing doesn't mean there isn't concern. But my point is more in regards to jacking the beam back up. I wouldn't do that if there is currently no damage to the finishes above, as jacking the beam would quite likely cause finish damage.

RE: 10x10 Timber Beam Sagging in century old home

So what does this two angles either side of beam look like? You have to transfer a good portion of the bottom side fiber tension in the beam to the angles in order for them to function as part of the beam. (Like tension rebar in a concrete beam), otherwise you just have two angles attached to a beam. How do you intend to make that transfer possible?

RE: 10x10 Timber Beam Sagging in century old home

(OP)

Quote (1503-44 )

So what does this two angles either side of beam look like?

Will have to pre drill the steel and anchor it to the beam using lag screws.

RE: 10x10 Timber Beam Sagging in century old home

I thought it might be something like that. I'm not sure how effective that will be. Drilling will remove a lot of wood from the beam tension fiber area. The discontinuiety introduced will tend to divert tension in the wood to go around the holes. Wood tension next to the screw is zero. What tension can be transferred to the screw when there is none there to transfer. Then looking at a hole that is essentially getting pulled into a longer oval shape, how will tension in the wood get to the screw? The wood is trying to pull away from the screw on each side. It seems to me that the only mechanism available to accomplish any stress transfer might be friction between the angles and wood beam surface, as you have no other bonding agent, such as cement bonding to rebar provides. Can lag screws apply enough force to the angles to develop enough friction to pick up the wood's fiber stress? How much? It would seem that glueing the angles to the beam would be better, but I have no idea if that would work either.

I've thought of using a tension bar placed just under a beam to try to make it work like a prestressed bar in a prestressed concrete beam, but located just next to, rather than inside the beam itself. You could then theoretically get enough tension in the rod to force the neutral axis down and even carry all the beams tension stress, leaving only compressive stress across the wood section. But then you have to anchor the rod to the beam and, with that high a rod tension load, that wouldn't be easy either. Maybe you could pass the rod through holes in clip angles located every 2 ft or so along the beam, screw the clips to the wood, stress the rod, then tack weld the rod to the clips. I still think you'd need some pretty hefty screws though.

RE: 10x10 Timber Beam Sagging in century old home

I suggest using threaded rods as shown in red each side of the timber beam. The rods at the two ends could be attached with steel plates fastened with glulam rivets. The sloping rods put an upward force on the short beams below the 10x10. The horizontal rod would be tightened with nuts and anchored with a lock nut. Sloping rods would need to be drilled through existing joists.



BA

RE: 10x10 Timber Beam Sagging in century old home

I can't see the advantage of sloped rods.

RE: 10x10 Timber Beam Sagging in century old home

Quote (1503-44)

I can't see the advantage of sloped rods.

I believe that sloping rods makes the connections to the beam a little easier, by riveting anchor plates to the sides of the beam instead of the bottom. Sloping rods provide a vertical reaction to the beam each side of the furnace, which a horizontal rod does not provide. One full length rod is probably not feasible because of basement clearances, but three rods would be more manageable.

If the end rods are horizontal, the connection to the beam could be a plate riveted to the underside of the beam, but the connection to the rods would be difficult. Could use a plate each side of the beam, but that would have to be designed as a moment connection to the beam, always difficult with timber.

BA

RE: 10x10 Timber Beam Sagging in century old home

This could work if there is sufficient clearance to get the rods in place. Otherwise, they would have to be spliced.



BA

RE: 10x10 Timber Beam Sagging in century old home

I was thinking the sloped rod would develop a very high tension because the distance to a supposed neutral axis decreases, as would happen in prestressed concrete design, no? But since it is not continuously bonded, you may be right in it acting more like a truss member. In that case the sloped rods load is set by the tension in the horizontal rod, and the beam starts to pick up the moment as we move from there toward the ends.

RE: 10x10 Timber Beam Sagging in century old home

N3M4N,

Could the OP place arrows on the pictures showing the location and length of the crack in the Beam, as I can not see this crack?

Is it also true that the crack does not go thru the entire depth/thickness of the beam?

Maybe my eyes are so bad that I can no longer read these photographs, but it seems to me that we are getting a lot of terrible photos.


Jim

RE: 10x10 Timber Beam Sagging in century old home

I interpreted the crack as shown below. The crack may not affect strength too much, but wouldn't hurt to give the beam a little help.

BA

RE: 10x10 Timber Beam Sagging in century old home

I'd at least put some wood filler in there.... doesn't look great.

RE: 10x10 Timber Beam Sagging in century old home

From the full basement photo, it looks like the furnace is over on the right side. So, the cracks in the first photo look to be happening near the beam bearing at the foundation wall.

If this understanding is correct, I’d suggest that you keep the post shown in the first photo (adding a footing if there isn’t one) and add a post on the other side of the furnace. The whole floor system looks like it’s been propped up with posts over the years, so one more won’t hurt. Shortening the span of the 10x10 would help most, in my opinion.

RE: 10x10 Timber Beam Sagging in century old home

Adding a footing under the existing timber post seems unnecessary as it is so close to the wall. It would likely be sufficient to add one adjustable telepost on the opposite side of the furnace. Bearing on the grade slab is not the best practice, but in this instance, may be a reasonable compromise.

BA

RE: 10x10 Timber Beam Sagging in century old home

(OP)
So after spending some time in the basement this weekend I removed the insulation that was tucked around the beam and noticed something really scary, the beam was not bearing on the foundation wall at all, it was toe nailed to the rim joist. Has anyone seen this kind of construction?

secondly, the ends of the beam were rotten pretty badly. Question, why was the rim joist not rotten?

Ended up with cutting 3/4" thick sheathing the width of the beam and placed under the beam at the ends. Moved the 4x4 post next to the foundation wall. As suggested I provided another 4x4 post on the other side of the furnace to shorten the span of the beam. I didn't jack up the beam as I didn't wanted to split the beam or the fragile joists. so the issue with the floor not being level is unsolved for now.

Here are some additional photos





RE: 10x10 Timber Beam Sagging in century old home

Misdirected perpendicular bearing shear looks like it is causing the checking splittage. The beams end is toast. It is going to need a large bearing area. Probably including a large cap on the post.

Personally I would consider a concrete column extended out from the wall.

RE: 10x10 Timber Beam Sagging in century old home

Quote (N3M4N; BAretired)

So after spending some time in the basement this weekend I removed the insulation that was tucked around the beam and noticed something really scary, the beam was not bearing on the foundation wall at all, it was toe nailed to the rim joist. Has anyone seen this kind of construction?
Not that I can recall. As you say, it is scary.

secondly, the ends of the beam were rotten pretty badly. Question, why was the rim joist not rotten?
The rim joist may have been protected with wood preserver (can't tell from the photo).

Ended up with cutting 3/4" thick sheathing the width of the beam and placed under the beam at the ends. Moved the 4x4 post next to the foundation wall. As suggested I provided another 4x4 post on the other side of the furnace to shorten the span of the beam. I didn't jack up the beam as I didn't wanted to split the beam or the fragile joists. so the issue with the floor not being level is unsolved for now.
The bearing condition at the end of the beam is even worse than before because of the dry rot. It might have been better to leave the existing post alone.

It would be best if the rotten wood could be replaced with sound material, but that would not be an easy thing to do. Hmm...needs more thought.

BA

RE: 10x10 Timber Beam Sagging in century old home

N3M4N,

Is there an update for this thread? Has the issue been resolved?

The rotten timber may have been caused by moisture attacking the wood. If the beam cannot be removed, at least the moisture source should be removed. Other locations should be inspected for the presence of timber rot as well.

Other timber beams should certainly be inspected to see whether or not they are bearing on the foundation wall as this constitutes a serious flaw in construction.

Removal of the timber beam over the furnace may be possible, but it would be difficult to accomplish. Methods can be discussed if you wish.

BA

RE: 10x10 Timber Beam Sagging in century old home

(OP)
BAretired,

I ended up placing 4x4 post on either side of the furnace to reduce the span of the beam. I inspected the other end of the beam and only one end is rotten.

what procedure did you have in mind to remove the main carrying beam, I personally don't think it can be done without removing the furnace first. each side of the beam has to be supported similar to removing a load bearing wall.

Let me know your thoughts.

RE: 10x10 Timber Beam Sagging in century old home

Removing the furnace is one possibility. Removing the beam from above is another. It would entail jacking the joists, cutting the deck, then cutting the beam out with a chain saw from above and replacing with a steel or glulam beam and providing joist hangers.

Neither approach is particularly appealing, but the rotten timber may continue to deteriorate over time.

BA

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close