Pipe Capacity Issue

Pipe Capacity Issue

Pipe Capacity Issue

(OP)
Hey everyone, I would greatly appreciate some assistance with the attached model. Specifically with node R7.

It appears that the model is allowing a much larger flow capacity through this run of 12" pipe @ 0.45% than possible.

Using Manning's equation, shouldn't the capacity for this pipe be limited to ~2.4 cfs VS the model allowing 4.61 cfs?

I am not sure why this is happening, but the main reason I am concerned is because the downstream system may need resized if the pipe capacity is actually overburdened as anticipated.

Thanks for taking the time to assist!

RE: Pipe Capacity Issue

The HydroCAD culvert analysis is not just simple Manning's flow. It also considers headwater, tailwater, and entrance losses. If you apply enough head, you can push any amount of water through a culvert. Have a look at the stage-discharge curve and you can see the behavior as it transitions to pressure flow at about 2.4 cfs.

I you wanted to use strictly Manning's flow, and ignore the other factors, you could use a pipe reach. But your solution (a zero storage pond with culvert outlet) is much preferred, because it properly simulates the results under a much wider range of conditions.

For complete details please see www.hydrocad.net/pipes.htm

Peter Smart
HydroCAD Software
www.hydrocad.net

RE: Pipe Capacity Issue

(OP)
@psmart

Thanks for the info. My issue really is the fact that typically when the program typically forces the water through the pipe I am used to seeing the error that the culvert has surcharged and am not seeing that here. I see that the flow is pressurized upon reaching a 'flowing full' scenario and then starts jetting through the culvert.

So, because the outlet of this system is actually into an existing system, do you think I should utilize the reach node type? My ultimate goal is to ensure that the flow into the downstream system (downstream of the proposed detention pond) is being adequately controlled by the detention pond.

With the current design and output data, I am thinking that this 12" outlet pipe is insufficient to pass the flows being minimally controlled by the pond and thus:
  1. The existing system needs to be upsized to handle the increased flows; Or,
  2. The proposed detention pond needs revised to control more of the flow.

RE: Pipe Capacity Issue

A submerged culvert inlet is properly handled by HydroCAD, so no warning message is generated. However, the user definitely needs to check the peak headwater elevation to ensure this meets your design criteria. That's one of the reasons for setting a flood elevation. You can use it to identify a submerged inlet - IF that's a condition that YOU would like to avoid. But it's not a problem for the software, which will continue to calculate properly for a submerged inlet.

To your question, I do not recommend a pipe reach, since it cannot handle potential tailwater effects. A culvert is better. If you want to avoid surcharging, simply check the headwater. The adequacy of the pipe depends entirely on your design criteria and the amount of headwater you choose to allow. If you want to reduce or eliminate the headwater, then you will probably want to use a larger culvert.

Since you are discharging into an existing system, you may also need to consider the tailwater at that confluence.

Peter Smart
HydroCAD Software
www.hydrocad.net

RE: Pipe Capacity Issue

(OP)
Ok, I understand, and thank you again for the assistance.

I switched the final reach node in my model to a pipe. I did this in order to model the run of the existing system to see this proposed system's effects.

HydroCAD was able to produce a message that node 33R peak inflow is 178% of Manning's capacity.

This is what I needed to see and be able to document.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close