Seawater submersible (1.5 meter) low voltage power cable.

Seawater submersible (1.5 meter) low voltage power cable.

Seawater submersible (1.5 meter) low voltage power cable.

(OP)
Gang, I have an application for a 50-meter 460 V cable run subgrade in ASSHTO class heavy grade precast concrete culvert with cast metal grate. The area is subject to periodic storm flooding to about 5 feet over grade. Many of the US cable manufacturers are telling me that their standard above-grade products, such as DLO, Exane, Type P, etc can perform underwater, despite there being no subsea rating. One manufacturer who makes subsea MV cable indicates they can also modify their run without problem and make their low voltage product, water-tight. Can anyone recommend an LV subsea cable?
A side question, is there any reason I'm missing why I can't run an MV subsea cable for LV service?



RE: Seawater submersible (1.5 meter) low voltage power cable.

Quote:

A side question, is there any reason I'm missing why I can't run an MV subsea cable for LV service?
Cost?

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!

RE: Seawater submersible (1.5 meter) low voltage power cable.

Moisture absorption seems like an issue for most thermoplastic cable insulations involving immersion. Thermoset materials perform better. Cross-link polyethylene cable works well in immersion.

RE: Seawater submersible (1.5 meter) low voltage power cable.

If this is an active storm drain that can pass flowing water, the cable may need to handle the mechanical loading that might result from the flowing water.
Tugboat's observation about permeability of insulation is the same as mine. Below grade conduit systems often are full of water, and sometimes mud, so water resistance is almost always necessary. The result of picking a moisture permeable insulation is conductor corrosion.

Fred

RE: Seawater submersible (1.5 meter) low voltage power cable.

(OP)
Cost is not a great issue in that the alternative would be to run an overhead bus duct, and I would normally select to run an overhead bus duct in this case but for the heavy machinery traffic and vulnerability of the posts supporting the bus duct structure - ergo the subgrade approach.

The concrete culvert is not an active storm drain in the sense of its primary intention but will drain rainwater, sheet flow, and of course, receding floodwater. Additionally, the width of the culvert is about 48 inches and the cables will be elevated several inches off the bottom.

RE: Seawater submersible (1.5 meter) low voltage power cable.

I believe cables meant for immersion will have a layer of water blocking tape under the jacket.

https://geca-tapes.com/applications/power-cable/

I would look in to a marine class society approved (American Bureau of Shipping or DNV are the leaders) cable with low smoke insulation. The low smoke cables typically use some type of TPE or CPE insulation and are available with the water tape. The cost should be reasonable if you get it without armor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close