If you have read this far you will probably enjoy this link to the entire Wiki article. Ufer GroundsWiki said:History
During World War II, the U.S. Army required a grounding system for bomb storage vaults near Tucson and Flagstaff, Arizona. Conventional grounding systems did not work well in this location since the desert terrain had no water table and very little rainfall. The extremely dry soil conditions would have required hundreds of feet of rods to be driven into the earth to create a low impedance ground to protect the buildings from lightning strikes.
In 1942, Herbert G. Ufer was a consultant working for the U.S. Army. Ufer was given the task of finding a lower cost and more practical alternative to traditional copper rod grounds for these dry locations. Ufer discovered that concrete had better conductivity than most types of soil. Ufer then developed a grounding scheme based on encasing the grounding conductors in concrete. This method proved to be very effective, and was implemented throughout the Arizona test site.
Construction
Concrete is naturally basic (has high pH). Ufer observed this meant that it had a ready supply of ions and so provides a better electrical ground than almost any type of soil. Ufer also found that the soil around the concrete became "doped", and its subsequent rise in pH caused the overall impedance of the soil itself to be reduced.[2] The concrete enclosure also increases the surface area of the connection between the grounding conductor and the surrounding soil, which also helps to reduce the overall impedance of the connection.
Ufer's original grounding scheme used copper encased in concrete. However, the high pH of concrete often causes the copper to chip and flake. For this reason, steel is often used instead of copper.
When homes are built on concrete slabs, it is common practice to bring one end of the rebar up out of the concrete at a convenient location to make an easy connection point for the grounding electrode.[4]
Waross said:NEC has gone the other way and now calls Ufer Grounds CEEs, Concrete Encased Electrodes.
I will continue to remember and honour Mr. Ufer by calling CEEs Ufer Grounds.