Isolation valve(Block Valve) installation for Rupture Disk & PSV
3
Dears
I need your advice for below query.
In our plant Drum is protected by One PSV & One Rupture Disk. Can we install isolation valve before the Rupture Disk? It is allowed by code? We have another Drum protected by multiple PSVs & RDs, isolation valves are there, and there is no issue. We received a request to install isolation valve for single PSV & RD, which is installed to protect the Drum.
RE: Isolation valve(Block Valve) installation for Rupture Disk & PSV
Not usually no.
A RD is there to protect against very large volume events which the relief valve can't handle.
The PSV is there to protect against small volume events without destroying the RD.
If you've only got one then by installing a valve you then have no protection from one or the other event.
Multiple ones allow one to be closed whilst maintaining protection as the other can't be closed at the same time (either by procedure or interlocks).
I would refuse the request.
ASME VIII (2019) Non Mandatory Appendix M-5 - States that a 'Stop Valve' in the relief path is not allowed unless certain conditions are met as detailed in this appendix,
ASME I (2019) PG-71.3 Does not allow any 'valve of any description' between vessel and safety valve.
Per ISO-4126, only the term Safety Valve is used regardless of applicatin.
Thanks for your feedback
Installing isolation valves under relief devices is a practical necessity in most cases. And it's an acceptable practice (except for ASME Sec I boiler applications) as long as you implement high-integrity administrative controls (e.g. seals or locking devices on valves) for managing those isolation valves.
The inability to isolate relief devices creates a high plant-reliability risk. Also, the inability to isolate a relief device creates potential safety risks when relief devices are pulled (insufficient vessel clearing, or accidents that can occur during that clearing process).
Having isolation devices under relief devices is a safety risk, but it's one that can be safely managed. And when you consider all the risks (safety and plant operability) associated with not having isolation devices, this is a pretty easy decision for large processing facilities.
Depends on the service of the drum, whether this PSV is for firecase or operational emergencies, its criticality in operations, and plant operating culture for this plant. Sometimes, you have block valves both up and downstream, some times only downstream, sometimes only upstream and sometimes none at all. You havent told us enough. Also read up the sparing and isolation philosophy design report for this plant, if there is one.
a valve in front of a rupture disk?
she go boom!
www.MaguffinMicrowave.com
Maguffin Microwave wireless design consulting
It standard practice our our industry to have N+1 burst disks and isolation valves under each disk. The isolation valves are locked open and have high-integrity administrative controls. Only one valve can be closed at a time.
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
The Great Project Profitability Debate
A/E firms have a great opportunity to lead the world into the future, but the industry’s greatest asset—real-time data—is sitting wasted in clunky, archaic ERP platforms. Learn how real-time, fully interactive dashboards in a modern ERP allow you to unlock data that will shape the future of the world. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close