Lateral Bracing Pony wall
Lateral Bracing Pony wall
(OP)
Hi there,
To lateral brace the pony wall as shown in picture with joist, can I use 2' galvanized strap on outside sheathing coinciding joists web with pony wall stud keeping bottom of the joist as the center of the strap. Or can I use A23 Simpson clip connect joist(bottom) with pony wall stud. Height of pony wall is 1 feet. Wall above floor is 9 feet high. Please advise
To lateral brace the pony wall as shown in picture with joist, can I use 2' galvanized strap on outside sheathing coinciding joists web with pony wall stud keeping bottom of the joist as the center of the strap. Or can I use A23 Simpson clip connect joist(bottom) with pony wall stud. Height of pony wall is 1 feet. Wall above floor is 9 feet high. Please advise
RE: Lateral Bracing Pony wall
You need to provide lateral restraint to the top of the concrete wall. We usually will install a line of horizontal wood strapping on the interior side along the top of the concrete wall. Then build a new wood stud wall on the interior side of the basement, tight to the strapping. You calculate the lateral load due to soil pressure on the concrete wall and use that value to design your stud wall. Anchorage of the stud wall to the basement slab-on-grade and anchorage to the floor framing above are the critical elements for this detail to work.
RE: Lateral Bracing Pony wall
RE: Lateral Bracing Pony wall
RE: Lateral Bracing Pony wall
The diagonal brace idea could work.
The interior stud framed wall is a common solution employed by many engineering firms in my area. One has the ability to modify the height of where the horizontal strapping is located (within reason) to balance out the shear and moment forces in the stud wall. Typical solution could be made to work with 2x6 @ 12" o/c or 2x8 @ 12" o.c. Connection details are important.
RE: Lateral Bracing Pony wall
RE: Lateral Bracing Pony wall
RE: Lateral Bracing Pony wall
In retrospect, we all wondered how anything could be framed or engineered so poorly.... An obvious hinge at the location of highest shear demand in the structure.
I'd be very wary of this type of framing. The best analogy I can give might be for the attachment of a tilt up wall to it's roof diaphragm. You've got a deflection compatibility issue where the wall is pretty rigid, but the diaphragm is not. Hence, there is a real tendency for the diaphragm to pull away from the wall and collapse in.
I like the idea of "fixing" this by using wood strapping or wood kicker braces. But, I would want these connections to really anchor into the wall. I might want them to be continuous to the other side, or dropped off in a way like we do for sub-diaphragms and such.
RE: Lateral Bracing Pony wall
Talking about the concrete walls, it's not a good practice to build concrete walls like this without wall anchors every 4'-0" o.c. to tie the floor/roof diaphragm to the top of the walls. However, if the thickness of the walls and their reinforcement are properly designed to resist out of plane seismic force (with 3 side supports being return walls and foundation), it should be ok. By the end of the day, if the movement of top of the wall is within limit, the floor framing won't fall down.
RE: Lateral Bracing Pony wall
I agree with those who write that there are shortcomings with this design and construction but.... I think the wall MIGHT perform fine. Not saying it'll work by the numbers but based on my experience I think the wall will span horizontally for much of the width. I don't usually see too much bad behavior until a wall gets closer to 30 feet and even then, it usually needs to be a completely straight wall (no offsets).
Still, I don't like it and it's a good idea to do SOMETHING to help it out.
Regarding the existing metal strap - a few additional picture (showing that detail up close) would help.
Since the metal strap doesn't work (become engaged) much until there is some deflection of the wall, it might not be such a great detail. I don't see how an additional strap on the outside will do much as the "tension" is going to be on the inside. If I understand the OP correctly, the inside is where there already is a metal strap. I assume that is an attempt to make the 12" stud was act like a cantilever up off of the top of the concrete wall. Again, it seems like much deflection will have to happen before this metal strap and wood stud mechanism will start to work.
An "interior stud wall" with contact at the top of the concrete and anchored well top and bottom is good but also not as effective near the corners.
Steel wide flanges installed vertically are "fine" but it's tough to resist the the horizontal force at the top with wood framing. (more so with the joist framing parallel to the wall)
Looks like the soil height might not be too high so maybe that helps keep the load down some too.
It's curious that there is some much blocking in the framing that is parallel to the foundation wall. I like that idea but I wonder what the philosophy was for how the load from the concrete wall is going to get into that blocking. If it was the existing metal strap then I wonder why the question. (just curious about how the OP got here.