Transfer Beam and Punching Shear
Transfer Beam and Punching Shear
(OP)
Hello,
In my project I have a row of columns, this row of columns should be supported in the beam.

My question is,should I consider / check punching shear in transfer beams
Point load = 2700 KN
Beam w / h = 100 / 110cm
Thanks in advance
In my project I have a row of columns, this row of columns should be supported in the beam.

My question is,should I consider / check punching shear in transfer beams
Point load = 2700 KN
Beam w / h = 100 / 110cm
Thanks in advance
RE: Transfer Beam and Punching Shear
I’d expect standard line shear will govern anyway if your column is any way reasonably sized.
RE: Transfer Beam and Punching Shear
the column is circular with diameter =35 cm
RE: Transfer Beam and Punching Shear
RE: Transfer Beam and Punching Shear
RE: Transfer Beam and Punching Shear
From most codes perspectives they state something like you only have an effective width of a wider beam at the joints and some of a wider beam might be considered ineffective (for both moment and shear). In ACI318-19 this is outlined in part in the dimensional limitations in CL18.6.2 (shown below). But for very wide beams that do not qualify with these provisions the code is a little silent. Clearly it can be wider, but not effective, but the question then is does it act like a two way slab, or other?
So they don't really cover to well is what to do if you want to consider the ineffective width on a wider beam as effective, for example you require the moment capacity of those bars right out on the edge of the beam to be effective, or to get the shear to work you need the full beam width considered and you might not meet the requirements of 18.6.2.
In this case you can use some judgement and detailing to add an orthogonal beam element to effectively pick up the shear from the ineffective part of the beam. In a way sort of like a corbel each side of the column but within the thickness of the beam, depending on the proportions you'd either design using strut and tie or normal flexural theory.
In your situation if you were following the ACI provisions to the letter, then with a circular column if you equated it to a square column of similar area to evaluate the dimensional considerations. Then the max effective beam width would be (1+0.75+0.75) x (π/6*350^2)0.5=775mm. So not all of the beam at 1000mm wide is effective. I'd make sure in this instance that you had sufficient orthogonal bars (and stirrups) through the column core in a similar manner to that shown in the figure below to pick up the shear outside the immediate width of the column (worked out on the basis that it is averaged over the width of the beam). This delivers the load to the column via this orthogonal beam element.
If you're just accepting that some of the beam is ineffective at the support, you need to be careful that you check the max shear provisions based on the effective width. In a way since part of the beam is considered ineffective the shear forces and moments concentrate into a narrower width at the column.
RE: Transfer Beam and Punching Shear
At the end of the day you need a sufficient number of shear legs crossing all potential failure surfaces - be it a 3D punching cone failure surface, or a 2D shear failure plane, or something in between. You don’t want the shear crack being sneaky and getting up and around your shear ties.
RE: Transfer Beam and Punching Shear
Note that Agent666's reference in ACI only applies to beam shear in Special Moment Frames, not Intermediate Moment Frames and would appear to apply to the column supporting the beam, not a transferring column. It appears to be very restrictive for deeper beams such as this one.
RE: Transfer Beam and Punching Shear
While that ACI clause is in the earthquake part of the code, since nothing exists elsewhere in the code eluding to the potential issues apart from the joints limitation in CL15.4.2.4, I believe you can apply similar logic for gravity cases as you fundamentally have similar behaviour with the load trying to get to the column and an effective width scenario ensuing unless you provide an alternative load path. All it is triggering is putting some thought into the situation when your beams are substantially wider than the columns.
I'm actually surprised that there isn't better guidance on this type of thing, but then you can't codify common sense and the need to consider all load paths that might ever exist. If you'd treat it any different then interested how you'd approach it in more extreme geometries with wider beams relative to column dimensions?
Irrespective of how you deal with it, I feel it's important to pickup that the load path is a bit more complex in a 3D sense as the beam gets wider relative to the column, than a simple 2D frame just transferring actions between a beam and a column.
It's more critical to deal with when you have people putting 0.5m diameter columns onto 2.5m x 0.6m deep band beams for example than the OP's arrangement (which sounds more within the bounds of it "will work" without much further consideration vs needing to do some more detailed analysis, design and detailing to establish a robust load path).
RE: Transfer Beam and Punching Shear
Agree entirely for wide band beams as you suggested at the end.
In those situations I have always provided a band of reinforcement in the top over the columns transverse to the beam direction for the beam load at the support to transfer the beam reaction at the support back to the column, basically as a double cantilever. To me that justifies using the full width of the beam for shear. I think you alluded to that in your first post.
When doing the calculations it comes out similar to the result you would get from some code requirements to place a minimum of the top reinforcement in the column strip of a flat slab within D either side of the column. I consider a band beam and slab floor to be basically a flat slab anyway as the band is not stiff enough to be called a beam and is really analysed and design as a slab thickening, like a continuous drop panel (in fact in the early DOS versions of RAPT it was defined as a continuous drop panel in the input!). So that code rule should apply to band beam and slab slab systems.
Unfortunately many do not listen when I suggest this! It was common practice in offices I worked in in the 1980's but seems to have fallen out of favor now that everyone relies on dumb computer software to do their design for them. But I am used to that.
My disagreement was with the very small extra width the ACI318 rule was allowing, independent of the depth of the beam. It seems unreasonably small. For an 1100 deep by 1000 wide beam with a 350 diameter column to only use 775mm width for beam shear is not logical to me for an 1100 deep beam! That is basically 200mm outside the width of the column either side. I would suggest someone on the code committee needs a rethink on that one and it needs to be depth dependent also.
The ACI rule is not for all seismic, only Special Moment Frames, so ductile moment frames (the kind us Aussies do not cover in our code and have to use NZS for!). It is not even required for Intermediate Moment Frames.
Then, a 350 diameter column seems awfully small for a transfer beam that needs to be 1000 * 1100. NZS would be limiting the flexural bar diameter to about 20mm for that support length!
RE: Transfer Beam and Punching Shear
Yeah I think you'd definitely have some issues with bond through interior joints. This often drives either bar size or alternatively column size
Don't read the NZ code then, it's even more restrictive in terms of the effective width to be used. From memory (don't quote me) it's quarter of the column width either side of column..... Still applicable for seismic though like ACI.
RE: Transfer Beam and Punching Shear
Looks like clause 9.4.1.8. But that is different. It is the width of the beam that can be assumed to resist the forces transmitted to the beam by the column!