Building Code= Fall Protection Guard (Cable)

Building Code= Fall Protection Guard (Cable)

Building Code= Fall Protection Guard (Cable)

(OP)
Hi!

I have IBC Code interpretation questions related with fall protection in the parking structure.
This case is happening in the precast concrete parking structure along the ramps.

My question is that fall protection cables are required along the ramps;
some small openings are located at the floor levels; about 30" wide x13" high at max.
In my opinion, these holes/openings are not big enough to cause pedestrian's fall protection problem.
Or, some fences can be installed only in the openings if they seem to be big.

Do you think protection cables should be installed along the ramps?

Thanks!

JRW


RE: Building Code= Fall Protection Guard (Cable)

I'd use the 4" sphere criteria - I could see somebody pull their three year old out of the car, set them down to grab a bag, and the kid runs over to stick their head through the hole...

RE: Building Code= Fall Protection Guard (Cable)

But to me, it's likely much easier to just fence off the openings than provide full length cables.

RE: Building Code= Fall Protection Guard (Cable)

It probably makes sense to close off the openings. A simple steel plate with post installed anchors installed 4" off the finished floor could work

RE: Building Code= Fall Protection Guard (Cable)

I think they should be closed off on the basis that someone could willingly jump out of one, either for the purposes of fun (BMX bike, skateboard, parkour) or escape (fleeing a crime scene, or possibly suicide).

Sorry if that seems grim, but I have a friend of a friend who jumped off of what I think was a parking structure. She did not survive.

RE: Building Code= Fall Protection Guard (Cable)

Quote:

In my opinion, these holes/openings are not big enough to cause pedestrian's fall protection problem.

I agree. It is there to warn the drivers for elevation drop, and protect pedestrian from tripping hazard.

RE: Building Code= Fall Protection Guard (Cable)

30"x13" is larger than some attic hatches I've crawled through. It most certainly is big enough to be a fall hazard.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

eBook - Functional Prototyping Using Metal 3D Printing
Functional prototypes are a key step in product development – they give engineers a chance to test new ideas and designs while also revealing how the product will stand up to real-world use. And when it comes to functional prototypes, 3D printing is rewriting the rules of what’s possible. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close