I am analyzing a wet gas pipe whose fluid comes from the upper outlet of a three-phase separator, followed by two compression phases. In the water extracted from the triphasic separator, the presence of APB and SRB bacteria was detected. Is the presence of bacteria a threat to the wet gas pipe? Are they able to be transported together with the gaseous phase and then grow from the condensed water?
Thank you!
Thank you!
RE: MIC Corrosion Wet Gas
Steve Jones
Corrosion Management Consultant
www.linkedin.com/in/drstevejones
All answers are personal opinions only and are in no way connected with any employer.
RE: MIC Corrosion Wet Gas
The use of periodic cleaning pigs is foreseen but I had doubts as to whether the microbiological issue should be considered (use of biocides) due to the absence of liquid water at the outlet of the separator. According to my previous ideas the bacteria could not be transported together with the gas phase but I wanted third opinions. Thank you very much for answering!
RE: MIC Corrosion Wet Gas
The bacteria will easily be transported in damp gas.
= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed
RE: MIC Corrosion Wet Gas
RE: MIC Corrosion Wet Gas
NACE Corrosion 2016, Paper 7194
Steve Jones
Corrosion Management Consultant
www.linkedin.com/in/drstevejones
All answers are personal opinions only and are in no way connected with any employer.
RE: MIC Corrosion Wet Gas
Presence of bacteria in the production fluid is alarming, though not uncommon. I would be investigate the source and cause of these bacteria in the production fluids. Contamination in reservoir is more alarming to me.