Absence of Electric Heater on Hydro Generator

Absence of Electric Heater on Hydro Generator

Absence of Electric Heater on Hydro Generator

(OP)
Greetings,
What could be some consequences of not having thermostat controlled heaters in the generator air housing? My concern is with condensation formation in the generator windings due to prolonged offline period during winter months. The unit is located indoors, but the indoor temperature is not maintained to setpoint.

Regards,
EE

RE: Absence of Electric Heater on Hydro Generator

You don't use a thermostat with an anti-condensation heater.
The heaters are typically connected for one half of rated voltage.
eg: 240 Volt rated heaters supplied with 120 Volts.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Absence of Electric Heater on Hydro Generator

The important thing is to keep the generator dry. Below freezing air can also be dry.

RE: Absence of Electric Heater on Hydro Generator

Bill said:

Quote:

You don't use a thermostat with an anti-condensation heater.

So true! A "thermostat controlled anti-condensation heater" is an oxymoron...

Think about it; the idea is to ALWAYS hold the temperature of the protected electrical equipment above ambient, no matter how high the ambient, and a thermostat would defeat the very purpose of the anti-condensation heater.

Anecdote:

One of the very well insulated metal-clad switchgear buildings at a transformer station in Toronto had healthily-sized anti-condensation heaters in the swgr cubicles, and on hot midsummer days when the outdoor temperature in the shade was 35°C the indoor temperature at that station could rise to 40-45°C - which was quite an incentive to expedite the completion of a station inspection. The protected equipment did however last for years and years.

As to the question in the OP: it depends on what other measures are undertaken to mitigate this concern...

Is the station structure an older one of poured concrete, block or brick? Or is it perhaps a newer one with a metal building envelope? The surrounding thermal mass can have a profound effect upon how quickly the internal temperature of the building changes, and therefore to what degree condensation can or does occur on the generator windings.

Is the plant run-of-the-river such that some units are always in operation 24/7, or does the plant operate using peaking/ponding such that a large number of units are in operation during the day and none are in service overnight? The latter case will cause much greater building internal temperature fluctuations than in the former...and in the latter, leap-frogging the units operated and closing the generator air dampers shortly before shutdown and keeping them closed until shortly after start-up can trap a good portion of the thermal energy in the windings and preclude or at the very least minimize the likelihood of condensation.

Do the units disperse their heat to the interior of the building with the building's internals subsequently rejecting heat to the ambient environment, or do the units reject heat directly out-of-doors?

More information yields better answers...

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Absence of Electric Heater on Hydro Generator

Also, depends how generators are cooled; if air within generator enclosure is constantly recirculated through dedicated air-to-[raw]water heat exchangers/coolers, leaving the cooling water flowing when a unit is off line for an extended period may be sub-optimal, as well as wasteful of water that could otherwise be used for power generation.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close