Dear Moonknight (Structural), the beam is UB254 x 146 . That is, (if there is no additional base plate ) , the bearing width shall be 146 mm.
If the reaction of UB254 x 146 140kN is factored load, and if the padstone is engineered brick fk= 13 MPa, Local strength = 1.25fk/(ϒm ) (for bearing type 1)
Local strength = 1.25*13/3= 5.4 MPa.
The bearing area will be Ab ≥ 140000/ 5.4 = 26000 mm2 Y=146 mm, X=26000/146= 180 mm. if the wall thickness t=440 mm,
Bearing length X ≥ t/2= 220 mm. Final bearing area Ab= 146X 220 mm . In order to determine the depth of padstone, we shall know the masonry wall blockwork strength.
Assume Blockwork strength 3.6 N/mm2 , Design compressive strength = 0.9*3.6/3=1.08 MPa. and the depth of the padstone will be determined using this Design compressive strength .
Assume there is only beam reaction load Ved= 140kN the area of the padstone will be = 140000/1.08=130000 mm2. If we assume the length of padstone y =440 mm (wall thk). the width x = 300 and bearing width 146 mm, with 45 degree dist. 73+ H= 150
H≥ 77 mm . round to H=100 mm .
Padstone final size= 220X 440 X 100 H.
This calc. for info only . the refined calc. shall consider available material properties and the other loads applicable to wall .