Cooling tower motor corrosion
Cooling tower motor corrosion
(OP)
I have been asked to look at adding cathodic protection to some cooling tower motors. Approximately one year ago the cooling tower structure was replaced with stainless steel. The motors mount directly to the SS. Since then the corrosion of the motor housing and the bare part of the motor shaft has been rapid. I am making inquiries about whether appropriate corrosion inhibitor is being used - presumably this is the case. The motors are run via VSD, but aside from that I do not know details of the electrical installation.
The photos show a motor back from refurbishment. This motor is not more than three years old. Apparently a better paint system has been used for the refurbishment. The cooling fins on the housing have corroded to be "comb-like" - I am not familiar with this. The corrosion on the bare part of the shaft is visible - the keyed part of the shaft should be a straight shaft. Below the shoulder, the material loss will be the same as immediately above. A coating has been applied to try and protect it.
My thoughts are:
- galvanic corrosion between motor housing and SS structure could be reduced by attaching an anode to the motor housing
- in addition, the motor shaft has electrolytic corrosion due to a shaft voltage caused by the VSD.
- A review of the chemical dosing should be done to ensure the use of corrosion inhibitors is adequate
Am I on the right track? Thank you
Note: Two photos are of a freshly overhauled motor. One is of a motor recently installed following the same refurbishment process.
The photos show a motor back from refurbishment. This motor is not more than three years old. Apparently a better paint system has been used for the refurbishment. The cooling fins on the housing have corroded to be "comb-like" - I am not familiar with this. The corrosion on the bare part of the shaft is visible - the keyed part of the shaft should be a straight shaft. Below the shoulder, the material loss will be the same as immediately above. A coating has been applied to try and protect it.
My thoughts are:
- galvanic corrosion between motor housing and SS structure could be reduced by attaching an anode to the motor housing
- in addition, the motor shaft has electrolytic corrosion due to a shaft voltage caused by the VSD.
- A review of the chemical dosing should be done to ensure the use of corrosion inhibitors is adequate
Am I on the right track? Thank you
Note: Two photos are of a freshly overhauled motor. One is of a motor recently installed following the same refurbishment process.
RE: Cooling tower motor corrosion
RE: Cooling tower motor corrosion
DHURJATI SEN
Kolkata, India
RE: Cooling tower motor corrosion
TugboatEng, I had wondered whether isolating the housing from the stainless frame could be an option.
Thanks also for the clarification on the cathodic protection. I had thought that a generally very damp environment would be sufficient - so good to not go mistakenly down that path!
The motors come from a reputable company - and the application would have been known. It is odd they didn't spec them more appropriately for the application.
RE: Cooling tower motor corrosion
Best regards - Al
RE: Cooling tower motor corrosion
RE: Cooling tower motor corrosion
https://www.baldor.com/cooling-tower-motors
RE: Cooling tower motor corrosion
Thanks - Al
Best regards - Al
RE: Cooling tower motor corrosion
This paper was useful: Direct Drive Cooling Tower Motor Paper: Link
In this case it does like the laminated fins do provide for cooling too.
The paper reinforced the need for a good paint system. I would think that once the laminations are exposed, all that potential extra surface area doesn't help with corrosion rates.
It'll be interesting to see how the new coating performs.