I have an Unbraced WF beam Pinned at both ends and a post at mid-span which places segments of both the top & bottom flanges under compression. Is it accurate to use the location of the infections points as the unbraced length (where the moment switches from + to -) or the total length of the whole beam?

Thank you
 
It is inappropriate to use the inflection points as a brace point.

You would use the full span length but use a Cb factor (per AISC) on the moment capacity.
Or you could add a positive brace at the inflection point, or anywhere for that matter, to limit the Lb.

 
Search "rafter without fly brace" in this forum [smile]
 
Do not use inflection points as braces. I believe this is even written in most codes. Inflection points aren’t 100% accurate.
 
Is the post above or below the beam? Is the post braced laterally? There might be more to evaluating the stability of this system than just a standard unbraced length check on the beam. All I know right now is you have a pin-pin (torsionally restrained at ends?) beam that is unbraced and is supporting a post - doesn't sound too stable to me.
 