Minimum Distance between pole base and Guy anchor
2

Minimum Distance between pole base and Guy anchor

Minimum Distance between pole base and Guy anchor

(OP)
I am wondering if there is a minimum horizontal distance requirement between Pole base (directly buried wood pole) and the guy wire anchor. I have seen few utility standards where they specify minimum 3m between each anchor, which I guess is to ensure the ground around each anchor is not compromised. I am curious if the same distance applies for the pole base to the anchor as well.

RE: Minimum Distance between pole base and Guy anchor

2
Ah, finally a topic I am familiar with.

Ground anchors (of the helical variety, as sold by Chance and Hubbell Power Systems) definitely receive a mandatory minimum distance between each other. This is a function of the burial depth and angle of friction in the soil which determines the 'cone of influence'. In my designs, these cones do not overlap.

However, I do not specify minimum distances between an embedded utility pole and the ground anchor. As a caveat, when the pole is short enough that the guy anchor will be 'close' to its base (i.e. inside the cone of influence) the loading is usually very minimal, and relatively small pull test values result, and I am not worried or concerned.

If for some reason the loading in the guy wire was substantial (10k tension or greater for example) I would perform a more detailed analysis to determine if I need to avoid any disturbed soil to reach my necessary capacities. Though, in my industry, the pull-test (performed according to my specific criteria) is the final word in anchor capacity.

RE: Minimum Distance between pole base and Guy anchor

(OP)
Thanks for the reply MR_E30. Would you be concerned about disturbing the soil close to pole as it may compromise the pole foundation?

RE: Minimum Distance between pole base and Guy anchor

OP, it would depend on what the installation method of the ground anchor is. Traditionally in the industry I work in the ground anchor is installed with little compromise to surrounding soil. An attachment is placed on the end of a skid steer and the anchor is twisted into the ground. In this case I would not worry about the pole foundation.

I have had contractors that wanted to scoop out a large chunk of dirt, put an anchor in the hole, and then backfill with dirt, or even fill the hole with concrete. In this instance I could become concerned with the pole foundation, depending on backfill practices and forces in the pole.

RE: Minimum Distance between pole base and Guy anchor

(OP)
Makes sense. Appreciate your response.

RE: Minimum Distance between pole base and Guy anchor

Consider the pole is sitting on a hinge at ground surface and the pull on the line to it is from afar. The farther the anchor is from the pole, the less the anchorage resistance is required. An anchor very close has to be much better under the same circumstances as to pull of the line from afar. Its a simple statics problem.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close