Running into a situation that the contractor would like to embed new electrical conduit into the existing elevated concrete slab ( 8" deep)
Any code section (ACI, NEC) has any requirements for the depth of the embedment?
Any code section (ACI, NEC) has any requirements for the depth of the embedment?
RE: Conduit to be embedded in existing concrete slab
Is this a slab on grade or a suspended structural slab?
RE: Conduit to be embedded in existing concrete slab
RE: Conduit to be embedded in existing concrete slab
They cut and trenched the soffit of the suspended slab overhead which was precast, pre-tensioned slabs. They severed numerous 1/2" dia 7-wire strands at midspan.
Emergency shoring installed and some very upset upstairs neighbors. Expensive error by he contractor that got him banned from every doing work on that condo building too.
Photo I took of one strand that got off 'light' - they only partially severed a few wires of the strand.
Be very careful in allowing the 'chasing' of any structural element.
RE: Conduit to be embedded in existing concrete slab
Mike McCann, PE, SE (WA, HI)
RE: Conduit to be embedded in existing concrete slab
RE: Conduit to be embedded in existing concrete slab
Sounds like this is a bid problem and not a structural problem. Did the electrician didn't carry rigid conduit for surface mount and wants to embed plastic and the GC is too weak to hold them to the bid docs, or the GC received a written proposal that was different from bid docs. If so the building shouldn't compromise its structure for contractor error.