Punching shear in underground garage in Santander, Spain

Punching shear in underground garage in Santander, Spain

Punching shear in underground garage in Santander, Spain

(OP)
Hello all,

I would want to present you a "text book" example of punching shear in the covering slab of an underground garage in Santander, Spain. The slab had over it a significant earth fill because there was a park and sport facilities over it.

You can see videos and photos in the links:
https://www.elmundo.es/espana/2020/01/13/5e1c23a42...
https://www.lavanguardia.com/sucesos/20200113/4728...
https://www.lavanguardia.com/sucesos/20200113/4728...

As they explain in the text (please use the Translate feature), the underground parking had always had water leak problems. This last summer it was waterproofed. Maybe the leakages were "helping" the structure to not sustain such a larger water weight load and not collapse.
Replies continue below

Recommended for you

RE: Punching shear in underground garage in Santander, Spain

Yep, classic punching shear failure:



Thanks for posting this failure.

RE: Punching shear in underground garage in Santander, Spain

From the photo, it looks more like "direct shear failure" than punching shear failure, as all the column seem sheared in mid length.

RE: Punching shear in underground garage in Santander, Spain

I think the thickness of the top layer soil is throwing off the perspective. If the columns sheared there additional bumps in the picture, and there would be exposed rebar from the columns. The slab looks thin, since it seems to conform to the cars it collapsed onto.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Punching shear in underground garage in Santander, Spain

IRstuff - you are correct, no beams. That's typical flat-slab construction. The slab is designed as a large plate with point supports at the column. The critical failure mode is just what is shown - punching shear, where the slab fails in shear and the column "punches" through the slab as it falls. It's really catastrophic in multistory construction, since the slab below can't handle the weight of the slab above as it impacts it, causing another punching failure, and so on until the building "pancakes" to the ground.

RE: Punching shear in underground garage in Santander, Spain

The think slab in the dirt pile looks like the walkway pavement. Look the adjacent garage (un-collapsed), the thickness of slab is quite impressive.

RE: Punching shear in underground garage in Santander, Spain

If the slab were that thick, I doubt you could get nearly 40 simultaneous punch shear failures; if a column punch sheared the slab, the cantilever would likely cause column buckles in the adjacent columns. I think what we see on the edges are beams. Moreover, I think a thick slab wouldn't conform to the cars it collapsed on; it would pancake the cars completely, just from the sheer weight and impact.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Punching shear in underground garage in Santander, Spain

Believe or not, in the 90's, I experienced a similar failure in Michigan - a huge under ground water holding tank that collapsed due to extreme hydrostatic pressure caused by an intense rain storm. The plant was undergoing maintenance, so the tank was empty, unfortunately the emergency generator and the sump system both failed, and the subdrain clogged, the built up pressure pushed columns upward and sheared, with floor slab crumbled to pieces, and the flat plate roof slab collapsed by gravity.

I am not saying it is occurring here, but the remnants of the columns in the photo remind me of that - column broken in the shaft due to compression. For punching shear failure, I'll expect to see columns with some slab remnants hanging, as the weak shear plane of slab is located at the column perimeter with a distance d/2 from column face.

Looks like we need a Spanish translator to settle the score then :)

RE: Punching shear in underground garage in Santander, Spain

The pictures from the first link are a bit disturbing; if the slab is as thick as it appears in several photos, one would think there would be more rubble around the rebar, and there would be large chunks still intact, but everything under the rebar is in tiny chunks, and the stuff above the rebar doesn't look that thick at all.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm

RE: Punching shear in underground garage in Santander, Spain

Photos below are extracted from pic provided by azcats.





Pay attention to deflected roof slab above. Could be photographic effect and lighting, the floor looks bulged too.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close