Shallow foundations: distribution of soil pressure with Eurocodes

Shallow foundations: distribution of soil pressure with Eurocodes

Shallow foundations: distribution of soil pressure with Eurocodes

(OP)
Hi,

I work in a French office and I have questions about foundation design with EC7 and EC2.

I'm studying column foundations with eccentricity to program an Excel sheet.
I configured Meyerhoff, trapezoidal and triangular pressure distribution for combined bending to verify the soil pressure under foundations.

Now I'm programming the reinforcement which is define by struts and ties method if the footing is rigid or bending moment if it’s not the case.

I found in several documents that the reinforcement in ULS is calcultated with a rectangular distribution of the pressure which means Meyerhof's method. But I don't know why.

In fact, with EC7 the pressure under the footing is verified with SLS and ULS. So, we usually start to verify SLS before ULS with EC7.
If we choose the triangular or trapezoidal method (depending on the value of eccentricity) for SLS to otpimize cross sections, is that correct to verify with Meyerhof in ULS? Is it not strange to mix the 2 methods even if SLS is an elastic calculation and ULS a plastic one? Or can we verify ULS with trapzoidal or triangular diagrams? And what about reinforcement? Is it correct to use Meyerhoff's method in SLS?

What is the best engineering practice?

Thank you in advance for your help, I'm a little bit confused about the choice of diagrams..

RE: Shallow foundations: distribution of soil pressure with Eurocodes

I believe not many people here are familiar with EC7 and EC2. A drawing/sketch indicating footing shape, and pressure diagram may draw more eyes and responses to your concerns.

RE: Shallow foundations: distribution of soil pressure with Eurocodes

(OP)
Thank you for the answer.
For a shallow foundation with bending moment in one direction we can have a trapezoidal or triangular soil pressure depending on eccentricity value :



The NF94-261 is an annex of Eurocode 7. We find that Meyerhof’s method can be used to simplify the distribution soil pressure under footings but it's unfavourable for cross section:



I'm studiyng shallow foundations with trapezoidal or triangular pressure distribution. I have to calculate reinforcement with this non uniform distribution but here are extracts (from french books) of pressure diagram used for it:

-Reinforcement with strut and ties's method:

-Reinforcement with bending moment's method:


For both methods, hypothesis of soil pressure is the same: it is a rectangular diagram. How is it possible to take this hypothesis if the cross section of the footing was previously designed with a triangular or trapezoidal pressure distribution ?

I can't find any example of a shallow foundation reinforcement designed with a non rectangular soil pressure diagram...

Here is another extract from an english document which describes the diagram of pressure distribution for each limit states:

But i don't know how this choice is justified?

Thank you for your help.

RE: Shallow foundations: distribution of soil pressure with Eurocodes

If you noticed and understood the difference of the two abbreviations describing the pressure diagrams in the last graphic, you shouldn't have puzzled over which method is justified for 1) bearing pressure checking (an exact analysis), and 2) footing reinforcing design (an approximation/simplification to produce most conservative design). Make sense?

I personally don't like strut and tie method, with the exception of checking shears in deep concrete members. But the French method seems interesting.

RE: Shallow foundations: distribution of soil pressure with Eurocodes

(OP)
Thank you for your answer. This is why I’m asking I’m not sure to understand.
My question is, if reinforcement methods are not describ for a linear diagram( trapezoidal or triangular) and only uniform, is there any sens to optimize the cross section of shallow foundations with trapezoidal and triangular methods for geotchnical checking? It seems that finally we have to choose Meyerhoff diagram to have a coherence for geotechnical and concrete checkings, right?

RE: Shallow foundations: distribution of soil pressure with Eurocodes

In my opinion, there's no contradiction in using different diagrams for SLS and ULS conditions as the strain level is fundamentally different. More or less like RC section analysis, where you use a triangular stress strain diagram for service conditions and a rectangular stress block for ULS design.

RE: Shallow foundations: distribution of soil pressure with Eurocodes

Lhi,

I see your discipline is "geotechnical", so you understand well that soil never behave in any way "linear", nor "uniform", therefore, both diagrams (of SLS and ULS) only represent the best approximations that are quite close to the ideal responses of soil, yet remain easy for computation purpose.

The structural engineer like to think the soil is an elastic medium, thus, under service load, the stresses are derived through p = F/A +/- M*y/I, the resulting pressures are linear in forms of triangular or trapezoidal shape. The pressures are consider the exact (not true) solutions of the given conditions, they are then used in calculating the resultant force (R), determine its location under the footing base in contact with soil, and finding eccentricity (e) between the applied load and the resultant force. The maximum pressure and resultant force are thereafter to be used to check the serviceability requirements - namely, bearing pressure, overturning stability, and shear friction between footing-soil interface. This analysis method used to be called "limit equilibrium method", now is more clearly named as "service limit state" (SLS).

Although the primary usage of pressures stated above is checking serviceability, there is nothing wrong to use the pressures in design the footing depth and reinforcing. The dilemma lies in how to properly apply load factors as required in reinforced concrete design by ultimate strength method, a long heated debate I don't want to bring it up in here again. Thus, the uniform pressure distribution is a simplification that more suitable for the purpose of footing design (thickness and reinforcing). The name "ultimate limit state" (ULS) states its intend application clear and loud.

RE: Shallow foundations: distribution of soil pressure with Eurocodes

(OP)
Thank you for your help.

@retired13 I agree, thank you for your explications. (I made a mistake when I create my account, I'm structural engineer; I will correct it right away winky smile).

RE: Shallow foundations: distribution of soil pressure with Eurocodes

I'm not familiar with the Eurocode, so please keep in mind that my responses will be as per US code.

First, soil behavior is more "plastic" at the ULS, while it exhibits a more linear behavior in the SLS. That is why the load distribution assumptions changes between both limit states.

While I can understand why the use of the ULS limit state makes sense (as the load distribution would most likely resemble the ULS distribution during high loads), it is interesting to note that the AASHTO code states that the structural design should be performed based on a trapezoidal (or triangular) distribution.



At the end of the day, an assumption has to be made on whether (at the point at which the structural failure would occur on the footing) the load distribution is closer to plastic or to elastic. My completely unsubstantiated opinion is that, because AASHTO has a much more conservative resistance factor (φ) for bearing pressures than for concrete in bending, they assume that the soil will be mostly elastic at the point of structural failure. That being said, you'll have to use whatever assumptions/models your building code states.

RE: Shallow foundations: distribution of soil pressure with Eurocodes

It is my opinion, that except for some cohesive soils, the soil under load will not become plastic, it just settles more until a new equilibrium is reached.

Also, the soil does not know the acting load is "service load", or "ultimate load", it just settles less or more. However, in anticipation of larger settlement at the ultimate state, the allowable bearing stress was given (by GT) with a safety factor greater than the load factors to be applied in the ULS, to ensure in-situ soil capacity will not be exceeded at either case (SLS or ULS). This paragraph is open to comments from the geotechnical engineers.

I don't know why AASHTO sticks with the design using factored pressures derived through limit equilibrium method (I think BridgeSmith could provide insight on this). It is awfully difficult to track effect of each load, and maintain the location of the resultant force as determined by non-factored (service)loads. It had been a lengthy debate on this, at the end of the day, for practical reasons, most engineers either resorted to using the uniform (simplified) pressure diagram, or derive a single (weighted) load factor to be applied to all of the service loads. Many of the old structures, designed by any method mentioned above, still stand. So, judge yourself, which is better.



Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - Strategies to Secure Connected Cars with Firewalls
White-hat hackers have demonstrated gaining remote access to dashboard functions and transmissions of connected vehicles. That makes a firewall a vital component of a multilayered approach to vehicle security as well as overall vehicle safety and reliability. Learn strategies to secure with firewalls. Download Now
White Paper - Model Based Engineering for Wire Harness Manufacturing
As complexity rises, current harness manufacturing methods are struggling to keep pace due to manual data exchanges and the inability to capture tribal knowledge. A model-based wire harness manufacturing engineering flow automates data exchange and captures tribal knowledge through design rules to help harness manufacturers improve harness quality and boost efficiency. Download Now
White Paper - What is Generative Design and Why Do You Need It?
Engineers are being asked to produce more sophisticated designs under a perfect storm of complexity, cost, and change management pressures. Generative design empowers automotive design teams to navigate this storm by employing automation, data re-use and synchronization, and framing design in the context of a full vehicle platform. Download Now
eBook - Simulation-Driven Design with SOLIDWORKS
Simulation-driven design can reduce the time and cost of product development. In this engineering.com eBook, we’ll explore how SOLIDWORKS users can access simulation-driven design through the SOLIDWORKS Simulation suite of analysis tools. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close