(n) pad inside existing residential S.O.G.

(n) pad inside existing residential S.O.G.

(n) pad inside existing residential S.O.G.

(OP)
Hi All,

I need to introduce some interior pad foundations inside an existing residential remodel. What are some best practices with respect to breaking the vapor barrier?

I do not know yet if there is a vapor barrier but assuming there is, the installation of a new pad will break the barrier. Could this be sealed up during the new foundation pour say in two phases? First pour being the thickness of the new foundation. then phase 2 to include 2" of sand under new vapor barrier under the new s.o.g.?

Or is breaking the vapor barrier for such a small area (say 3x3 feet)not considered much of an issue?

Thanks all for your feedback and expertise

RE: (n) pad inside existing residential S.O.G.

Correct me if I'm wrong, but you want breach the slab and existing vapor barrier to set new footings? They way I do it can be summed in one word: carefully. Also, I don't pour footings on top of the existing barrier. Make your 3x3 opening and remove the rubble, taking great care to not shred the existing barrier. Once exposed, try to slice it corner to corner, and pull the 4 triangle flaps back and secure. Excavate your hole. Cut and attach new barrier material to the existing flaps (trimming as needed) to create square flaps instead of triangles. Right before the footing pour, tape up the interior corners of the barriers (think of it as recreating a paper bag from a bag that had its four vertical edges sliced open). Pour your footing up to the underside of the existing slab. Set your post (if it is a post). Re-cut the barrier and snug it up to the sides of the new post, and re-tape it all. Pour the topping slab after the footing sets.

RE: (n) pad inside existing residential S.O.G.

(OP)
Thank you PG67,

Would you have any resources you could direct me to look into about this topic? This has been a gray area to me for some time and want to make sure i have my bases covered

RE: (n) pad inside existing residential S.O.G.

(OP)
anyone else have experience with this or have go to details/procedures to reseal the vapor barrier?

RE: (n) pad inside existing residential S.O.G.

The only other option I can think of is to cut a larger than needed hole in the slab (maybe by a foot) without damaging the barrier. Then cut the barrier to the size of the new footing, excavate and pour the footing, and install your column. Once the dead load is applied, backfill to the bottom of the barrier. Install new barrier material lapping the edges of the existing and taping properly. Pour back you slab and you're done.

If you damage it and can't lap it from above, you'd have to undermine the slab slightly to access it and do something from underneath. Not sure how you'd accomplish that...so try not to mess it up!

RE: (n) pad inside existing residential S.O.G.

Lap the vapor barrier? Just tape it. I would drill a pilot hole to see how deep the slab, then sawcut a little less than this and jack hammer away. That should leave the vapor barrier in good enough shape to tuck tape it to new vapor barrier on top of your footing.

RE: (n) pad inside existing residential S.O.G.

Why a vapor barrier anyhow? Is there a high water table there and moisture in the room a problem? Most so called vapor barriers are damaged during installation. If you truly want a water-proof vapor barrier, ordinary plastic won't do it. Remember moisture vapor goes from warm to cold zones all other things equal. If a real concern the guides above suggest about the best that you can do and don't be expecting any great results.

RE: (n) pad inside existing residential S.O.G.

Agree with OG on all points.
For virtually all residential floor slabs, a vapor barrier is not going to stop water if the water table is the problem.
Dig a test hole and see where water level is. I suppose it might be a seasonal condition but if there is no history of water intrusion, I don't think it would be adversely affected by such a move. An under slab sump would probably be more effective IF something is needed.

Generally, I simply require excavation below the sub-base by several inches to reach firm and undisturbed soil and the new footing can be flush with the surrounding slab. Often, that results in a thick footing that might not even require reinforcing. 3 ft square might but that rebar would be incidental.

I don't recall ever requiring attention to the vapor barrier for a new footing in a residential basement renovation.

RE: (n) pad inside existing residential S.O.G.

Is the pad to be provided in the ground floor, or the basement? If not an obstruction to living space, have you investigated the possibility to add pad on the SOG?

Vapor barrier is to keep damp out of the floor, it has nothing to do with ground water. If necessary, the suppliers website shall have information on how to repair/seal it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - Strategies to Secure Connected Cars with Firewalls
White-hat hackers have demonstrated gaining remote access to dashboard functions and transmissions of connected vehicles. That makes a firewall a vital component of a multilayered approach to vehicle security as well as overall vehicle safety and reliability. Learn strategies to secure with firewalls. Download Now
White Paper - Model Based Engineering for Wire Harness Manufacturing
As complexity rises, current harness manufacturing methods are struggling to keep pace due to manual data exchanges and the inability to capture tribal knowledge. A model-based wire harness manufacturing engineering flow automates data exchange and captures tribal knowledge through design rules to help harness manufacturers improve harness quality and boost efficiency. Download Now
White Paper - What is Generative Design and Why Do You Need It?
Engineers are being asked to produce more sophisticated designs under a perfect storm of complexity, cost, and change management pressures. Generative design empowers automotive design teams to navigate this storm by employing automation, data re-use and synchronization, and framing design in the context of a full vehicle platform. Download Now
eBook - Simulation-Driven Design with SOLIDWORKS
Simulation-driven design can reduce the time and cost of product development. In this engineering.com eBook, we’ll explore how SOLIDWORKS users can access simulation-driven design through the SOLIDWORKS Simulation suite of analysis tools. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close