Hanging Pipe in PEMB

Hanging Pipe in PEMB

Hanging Pipe in PEMB

(OP)
I have a piece of industrial duct pipe (12" Sch 10) that will hang from the roof of a PEMB. ASCE 7 doesn't give much guidance on this sort of thing, so I wanted to ask if anyone here can point me in the right direction.

Initially, I supposed I would put a vertical hanger with a diagonal to keep it from swinging wildly in a seismic event.

I can't imagine this hasn't been done before...

Thanks in advance for any help.


-5^2 = -25 winky smile

http://www.eng-tips.com/supportus.cfm

RE: Hanging Pipe in PEMB

I have dealt with this issue exactly one time, back in the late 1990s.

My task--sprung on me with one day's notice by my project manager--was to inspect all of the seismic bracing for all of the hanging pipes and ducts in the new headworks buildings at the local wastewater treatment plant. The headworks building is eight stories tall (half underground) and bigger than a football field. My task was to learn the requirements (I was starting from zero) and do the inspections over the weekend, so that come Monday morning the City could issue itself an occupancy permit. Needless to say, I was p*ss*d since I had plans for the weekend.

For guidance, my project manager handed me a copy of the SMACNA Seismic Restraint Manual, and that's the document you need. With SMACNA, the plans and specs, and binoculars, I got through the entire headworks in one long weekend. I needed the binoculars because some of the hanging pipes and ducts were more than thirty fee up.

I found so many problems, that the City couldn't issue itself the occupancy permit on Monday. It took the contractor more than a week to fix everything that I found was wrong.

==========
"Is it the only lesson of history that mankind is unteachable?"
--Winston S. Churchill

RE: Hanging Pipe in PEMB

Seismic bracing is common in California. Many manufactures have typical details. Probably not one specifically for 10” schedule 10 duct. But, they have details for pipe or round duct that can be adapted. A few manufacture off the top of my head are: Unistrut, Tolco/B-Line, Mason Industries, ISAT, Anvil, PhD . . .

RE: Hanging Pipe in PEMB

What part of ASCE 7 were you looking at? Chapter 13 is all about non-structural building components subjected to seismic loading, with about half the chapter dedicated to plumbing/mechanical systems and their anchorage.

My concern is that it's being hung in a PEMB. Is this a new PEMB or an existing one? A 12" pipe can get pretty heavy when full, and those buildings are designed as lean as possible. I've checked them for the addition of a lightweight RTU (essentially a little residential unit) and couldn't justify it - we had to install columns from the floor to reinforce it.

RE: Hanging Pipe in PEMB

As a side note, if you are adding the pipe to the PEMB, suggest you run the additional load by the EOR if you have not already done so.

PEMB's are notorious for being super sensitive to any increase in load, especially is the 12" pipe is filled w/ any sort of fluid.

RE: Hanging Pipe in PEMB

(OP)
Thanks for the replies.

We did work through Chapter 13 and I couldn’t quite nail this one down. The pipe is dust collector exhaust ducting, so there is no liquid load. The PEMB manufacturer listed a collateral load of 5 psf - we are below that globally and have checked the individual members against details they provided for point loads.

We did find some proprietary products that will do the trick.


-5^2 = -25 winky smile

http://www.eng-tips.com/supportus.cfm

RE: Hanging Pipe in PEMB

Did you assume the pipe was 100% full of dust? Although dust is typically heavier than fluid (62.4 pcf), I believe you are granted some relief by assuming only a certain percent of the duct is full (can't remember off hand what percent).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

eBook - Functional Prototyping Using Metal 3D Printing
Functional prototypes are a key step in product development – they give engineers a chance to test new ideas and designs while also revealing how the product will stand up to real-world use. And when it comes to functional prototypes, 3D printing is rewriting the rules of what’s possible. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close