Help identifying a strange transient upon closing of a breaker
4
Hi guys!
I've looked around a bit to find a good forum to post this question, and after reading through a few other threads here I think I may have found the right one!
I was analyzing a disturbance we had in our distribution grid (20 kV) and while examining the TFR:s I found a strange transient in one of our feeders when reenergizing it after having removed the faulty cable. We have a couple of customer owned stations on this specific feeder and I can't really say what kind of setup they are running, except that they are customers on the medium voltage level and may have medium voltage loads other than transformers.
In the image one can see that the current transient on phase 3 seems to be half wave rectified, inductive and of fundamental frequency. It is, in fact, the inverse of the sum of the currents in phase 1 and 2, which is quite easy to see as the transient is dampened. The transient eventually dies out, but the load current on this specific feeder is quite dirty with harmonics and I will have to investigate it in more detail eventually. For now, though, I'm just really curious on what kind of load that may be causing this kind of transient. Any ideas?
Best regards,
Henrik
RE: Help identifying a strange transient upon closing of a breaker
Hi Henik,
This is a typical wave signature of magnetizing inrush current with small harmonic superimposed. This shown primarily during stating of the 3phase power transformer and decaying rapidly in a few seconds.
It looks good to me.
As cuky suggested, the inrush of a customer's transformer.
Bill
"Why not the best?"
Jimmy Carter
3
As said, it's transformer inrush, but it can be any number of transformers that were all deenergized simultaneously.
Transformer inrush is typically characterized as being random, and if it's truly random one might expect that the simultaneous energization of multiple transformers to have a muddled wave shape without the sharp characteristic seen in single transformer inrush captures. Where the randomness actually comes in is the point on wave where the transformer was last deenergized.
A feeder full of transformers that were simultaneously deenergized by the tripping of a feeder breaker will all have the same inrush characteristic if energized simultaneously by the closing of the breaker. It will look like the inrush of a single transformer. Next trip and close will produce a different point on wave and a different inrush waveform, but it will still look like a single transformer.
A good point and a good explanation David. Thanks.
Bill
"Why not the best?"
Jimmy Carter
How long does residual magnetism last in a transformer? How long does it take to decay?
Weeks at a minimum. It only leaves thru thermal activity.
Keith Cress
Thanks for your answers, everyone!
I guess we can consider this one solved. It proves that I still have a lot to learn about AC! (I have a background in HVDC)
Hello Henrik_S:
Be aware that the HVDC converter station is also subjected to inrush current and overshoot of the output voltage which could exceed far larger than the rated values. The good news is there is available technology to mitigate that.
Quote (ABB: Due to capacitors used in the HVDC converter, its energization produces a higher inrush current causing a severe voltage dip in both the ac and dc systems potentially exceeding the allowable limits. Similarly, dc cable and HVDC transformer energization also causes a higher inrush current that can damage the semiconductor devices used in the converter system.)
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
White Paper - How ESI is Helping Move New Medical Device Product to Market Quicker & More Cost Effic
Early Supplier Involvement has long been a strategy employed by manufacturers to produce innovative products. Now, it almost seems like a necessity. Because decisions made in the design phase can positively affect product quality and costs, this can help add value to OEM bottom lines. This white paper will discuss many facets of ESI, including why it’s so valuable today, what challenges limit the benefits of ESI, how cost is impacted, and more. Download Now
White Paper - Moving to a Driverless Future
This white paper describes what we see as the best practices to support a sustainable engineering process for autonomous vehicle design. It exposes how to use simulation and testing in common frameworks to enable design exploration, verification and validation for the development of autonomous cars at a system, software and full-vehicle level to drive a mature product development process for automated driving. Download Now
Research Report - How Engineers are Using Remote Access
Remote access enables engineers to work from anywhere provided they have an internet connection. We surveyed our audience of engineers, designers and product managers to learn how they use remote access within their organizations. We wanted to know which industries have adopted remote access, which software they are using, and what features matter most. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close