L-L-G VS L-G Fault Level

L-L-G VS L-G Fault Level

L-L-G VS L-G Fault Level

(OP)
Hi,

Between a L-L-G fault and a L-G fault which would you expect to give a higher MVA?

I am getting a study with a higher L-G fault level, but I though that the L-L-G fault level should be higher?

Thanks

RE: L-L-G VS L-G Fault Level

Location in the circuit? If it's near a transformer secondary, the L-G fault will be higher.

RE: L-L-G VS L-G Fault Level

See IEC 60909-0/2001:

RE: L-L-G VS L-G Fault Level

What type of installation is it (can we get a circuit diagram)?

If your installation is near the transformer on the secondary side then L-G should be the same as L-L-G, this is of course under the pretence that all the impedances are equal.

However! Since both L-G and L-L-G are dependent on the zero sequence they are therefore both dependent on the return path for the fault and the transformer/source earthing.

If we strictly look at the equations assuming E is the phase pre-fault voltage they will look like this:





A note about the L-L-G fault, The left and right hand side of the equation corresponds to a faulted phase, so let's say fault current in phase b corresponds to the left equation and phase c to the right equation. Then from a strictly mathematical perspective if Z0 is greater than Z1 or Z2 if they're equal. Then one phase will have a higher fault current than the other, which can be verified in a simulation tool or by just doing the calculation, although they shouldn't vary greatly to a point where this difference is significant. Then there's an entirely different equation that calculates the fault current in the ground

However if all sequence impedances are equal then the L-G and L-L-G faults are equal.

If Z0 is 0, then L-L-G will exceed the L-G short circuit.

All of this however is speaking strictly from a mathematical perspective and not a practical perspective, as I don't have the amount practical experience the majority in this forum has.

The point I'm trying to make: Look at your circuit, where does the fault happen, what's the return path (does it have a high or low impedance?) and what's the system earthing. All of these factors will affect the fault current in the two scenarios you're examining.

RE: L-L-G VS L-G Fault Level

RE: L-L-G VS L-G Fault Level

If the transformer is WYE (high side)/ delta (low side)then the a L-L-G fault
current on the WYE side is higher than the L-G fault. Typical example is a WYE/delta
transformer connected to the Utility at small distributed energy resource (DER) stations.

RE: L-L-G VS L-G Fault Level

LLG fault is larger than SLG fault if the following conditions are satisfied:
1) 0.7 ≤ Z2/Z1 ≤ 1.0 and 2) 1.0 ≤ Z2/Z0 ≤ 1.4
The graph below indicates a linear approximation of the region were LLG fault is larger than SLG.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - The Evolving Landscape of Commercial Battery-Powered Trucks
What’s driving the evolving landscape of truck electrification? What are the barriers, motivators and strategies for accelerating the electric transition? What insights and resources are available for today’s design engineers working to achieve industry disruption and evolution? For answers to these and other pertinent questions, read this white paper. Download Now
eBook - Rethink Your PLM
A lot has changed since the 90s. You don't surf the Web using dial-up anymore, so why are you still using a legacy PLM solution that's blocking your ability to innovate? To develop and launch products today, you need a flexible, cloud-based PLM, not a solution that's stuck in the past. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close