Contactor failure

Contactor failure

Contactor failure

(OP)
Hi, let me get to the point right away, i recently was called to maintain a 160kva perkins generator with an ats that has two af 205-30 contractors for switching...and in my inspection one of the poles from the generator contactor has melted and so was not conducting at all, while the other two poles were working fine, along with the mains contactor,(i took a picture bzw). It would really be helpful if i had your insights as well,as the ats is new(only worked for three months), the load consists of an elevator with 600kg max, a 3hp pump, and lights for a house,( the generator controller did not trip any alarm which it would have done with overload and stuff. Can you help??

RE: Contactor failure

Bad connection.
The bolt may have not been tight enough, the jumper may not have been properly cleaned of aluminum oxide before being connected, if the contactor has replaceable contacts, the contact may not have been fastened securely.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Contactor failure

Almost certainly as Bill says above - bad connection.

I don't think that contactor has field-replaceable poles, but you should be able to carefully dismantle it to have a look inside and check for problems. Look for simple things like fragments of foreign material preventing correct operation, either by jamming the moving yoke or by preventing full contact on the pole face.

RE: Contactor failure

Good point Scotty. I have seen plastic contactor parts distorted by heat from a failure. I have also seen the full travel of a contactor compromised by foreign matter.

I have seen ATS contactors destroyed and contacts burnt off by closing in on too much load.
The load starts to stall the generator. As the speed drops the voltage drops. At some point the contactor drops out, pulling a heavy arc. With no load the set accelerates. The voltage builds up and the contactor re-closes. The cycle repeats. It only takes a few minutes to burn the contacts through to an open circuit.
I know of two instances and was able to avert the same problem in a lot of other installs.
When that happens, all contacts are damaged even if only one pole burns free.
In your instance, I am not sure of the load.
I have been looking for my old formula to convert 600 kg to KVA.
A couple of factors may be missing.
In any case, I doubt that it is enough to stall a 150 KVA set.

When replacing the contactor, remove the connecting jumper and clean it well of any corrosion. This includes both ends and the main bus where the jumper makes contact.

The screw fastening the jumper to the contactor may have been loose and started the failure sequence.
I have seen similar failures on circuit breakers.
Or maybe something else.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Contactor failure

(OP)
Thanks guys, its awesome to have ur insights

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

eBook - Integrating the Engineering Ecosystem
Aras Innovator provides multiple options for integrating data between systems, depending on the scenario. Utilizing the right approach to meet specific business requirements is vital. These needs range from authoring tools, federating data from various and dissimilar databases, and triggering processes and workflows. Download Now
Research Report - Simulation-Driven Design for SOLIDWORKS Users
In this engineering.com research report, we discuss the rising role of simulation and the paradigm shift commonly called the democratization of simulation. In particular, we focus on how SOLIDWORKS users can take advantage of simulation-driven design through two analysis tools: SOLIDWORKS Simulation and 3DEXPERIENCE WORKS. Download Now
White Paper - Industry 4.0 and the Future of Engineering Education
With industries becoming more automated, more tech-driven and more complex, engineers need to keep their skills and knowledge up to date in order to stay on top of this wave—and to be prepared for the Industry 4.0 future. The University of Cincinnati offers two online Master of Engineering degree programs designed specifically for practicing engineers. Download Now
eBook - The Design Gridlock Manifesto
In this eBook, you’ll learn 6 ways old CAD technology slows your company down and hear how design teams have put those problems to rest. “The Design Gridlock Manifesto” shares first-hand modern CAD experiences from 15 companies around the world. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close