Assistance choosing a 3-phase transformer to supply a CNC machine

Assistance choosing a 3-phase transformer to supply a CNC machine

Assistance choosing a 3-phase transformer to supply a CNC machine

(OP)
Hi everybody,

I'm a mechanical engineer trying to wrap my head around choosing a transformer for a new CNC mill coming into our shop. We're a small operation, so I have ownership of all the technical aspects of the purchase, nearly all of which are squarely within my professional experience. The 3-phase power, however, is a new frontier.

Of course, a real electrician will perform the installation, but I need to have a fundamental understanding of the situation in order to get quotes for the work. Also, the machine represents a significant investment for our shop, so we're proceeding very methodically.

Documentation provided by the machine tool maker seems weak, at least to a layman. A call to the applications department of a transformer manufacturer was little help. Most surprising is the amount of bad and dangerous advice online regarding machine tool wiring.

I greatly appreciate any education that you can provide. Please correct any errors of terminology without mercy. So, here's our situation:

  • Power company will supply our facility with 277/480 3-phase 4-wire wye.
  • Machine tool specs name a range of acceptable input voltage that is nominally referred to as 220 3-phase.
  • Machine peak power is 40kVA, maximum continuous power is 28 kVA. I'd guess that most people never use these machines at anywhere near these levels; we certainly won't.
  • We're considering a transformer rated for 75kVA to support future machine purchases.


  • The following points are taken directly from the machine tool documentation:
    1. The ground wire is required for operator safety and correct operation.
    2. A separate ground wire must be connected to the chassis of the machine.
    3. The ground wire must be supplied from the main building ground.
    4. Do not use a conduit as a ground wire.
    5. Do not use a cold-water pipe or ground rod to supply the machine ground buss
    6. Power can be Wye or Delta type.
    7. You must ground the power source. One leg or center leg for Delta. Neutral for Wye.
    I wish that their language was a bit more precise or that they provided a diagram. In any case, as a layman with little knowledge of the applicable NEC requirements, I draw the following conclusions:
    1. Transformer secondary could be either wye or delta.
    2. With a wye secondary, the center of the wye should be bonded to the equipment grounding conductor (EGC).
    3. With a delta secondary, either the center of one phase or the corner should be bonded to the EGC.
    4. The machine does not require a specific voltage between any phase and the ground lug of the machine.
    5. The EGC should be a wire and should run directly to the ground lug of the machine.

    These conclusions lead to more questions:
    1. It seems like there is no purpose for a "neutral" coming from the secondary of the transformer. Is this correct?
    2. Is there a reason to choose a particular primary arrangement, delta or wye?
    3. Is there a reason to choose a particular secondary arrangement, either delta or wye?
    4. If a delta secondary is chosen, since I don't need a particular phase-to-neutral voltage, is there a preferred method of bonding to the EGC, either center-of-phase or corner?
    This post is getting awfully long, so let me stop here for now. I have attached a diagram of my understanding of the situation. I welcome harsh criticism of that as well.

    I appreciate your help!




    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    I would use the wye secondary. It keeps the 3 phase voltages nice and balanced. The electronics in the machine will certainly appreciate it, even if the manufacturer claims it's not necessary.

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    While I agree generally with Hutz, if there is no place to land a neutral in the machine then there isn't much use for a neutral. Most machine tools do not have neutral landing posts. Some made for 200V (208V) do and that's so they can use the neutral and a hot to provide 120Vac to run all the controls without including a control transformer (cheap bastards I'd like to strangle half the time). (Mostly European tools.)

    If you indeed have three phase and are not using two windings (open delta) but three in a large floor mounted transformer, I'd go with that with one winding center grounded providing 120 to each end of the center tapped winding.

    That point on the grounded winding should be connected to the safety ground (bonding) it should be done there and only there. That secondary side of the transformer is called a "separately derived source". All separately derived sources must be referenced to something, preferably ground. Whatever that point is in the separately derived system becomes the neutral of that new system. From then on it is treated as a neutral and not a ground. The safety ground must continue as the safety ground in the separately derived source space.

    As for grounding:
    They're making much to do about nothing with regards to it.
    Yes, you definitely need one.

    It should come from the service entrance where somewhere very close an actual ground rod must be in place. Other grounds are available like UFER grounds which tend to be better than ground rods. A UFER ground consists of metal encased in concrete that is in direct contact with earth. Because of the immense surface area a UFER ground typically outperforms a mere copper plated steel rod by an order-of-magnitude. They do need to have a strong capable connection though, so unless you have a purpose-built one or you have big bolts projecting from the concrete, perhaps bolting down the walls with the bolts tied to rebar in the slabs you will probably have to use a rod.

    Often the ground wire can be smaller than the phase wires but I'd probably stick with the same size.

    Classically you're supposed to run wire 20% larger than the equipment plate to cater to the 80% NEC rule of over-sizing wiring so that it's not loaded more than 80% of rating for continuous use, which a machine tool could conceivably be left to do, running long periods at high loading. Some of the shops I service machine tools at run their machines unattended all night long and even over weekends.

    As I said 'classically' that's what you have to do to be 'code compliant' especially if you will be inspected. That said, many of the places I service wouldn't conceive of wiring their machines to the 80% rule and in fact wouldn't even consider 40% of the plate rating. They know their process and how loaded the machines are. I see dozens of machines in lineups with 60A 480V plates wired with 10AWG and 20A breakers. While in shock at such behavior I open the panels pull out a clamp-on and measure 5A. They inform me, "That's our biggest part we subject the machine to".

    My attitude is they're protecting the wire more than adequately. If they pull more, they'll drop the breaker and have a CNC mess to clean up, but it's not a fire hazard. It's actually more hazardous to plumb 60A to problem than 20A. But, you have to assess your situation knowing your..situation. If you do piece work and not production, down the road someone may want to hog out some huge chunk of tool steel and the machine might need a lot of power.

    Your drawing looks fine. I'd stick with the center path as shown.


    Keith Cress
    kcress - http://www.flaminsystems.com

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Keith, why is the TX required to produce 120V center tapped when the machine doesn't need it. I could be as dismissive of you recommending that as you were of me recommending the wye connection.

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    The center tapping wasn't for use with 'the machine' just as more useful 'for things' than a corner grounded. Though, with 480V it wouldn't matter. Now that I think of it the OP stated 480 but diagrammed 240.

    Keith Cress
    kcress - http://www.flaminsystems.com

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    (OP)
    Thank you both for the replies.

    LionelHutz, your reasoning for a wye does make sense; it certainly can't hurt that the 3 phase voltages are equal with respect to ground. I also read a source (random guy on internet) that claimed insulation life might be prolonged by avoiding the higher potentials above ground that result from a delta secondary. Is this anything more than a hypothetical concern?

    Quote (itsmoked)

    Whatever that point is in the separately derived system becomes the neutral of that new system. From then on it is treated as a neutral and not a ground. The safety ground must continue as the safety ground in the separately derived source space.

    This has me puzzled a bit. If the neutral of the secondary is bonded to the EGC inside the transformer enclosure, and two wires common to that point exit the enclosure, it's pretty clear what's a current-carrying grounded neutral conductor and what's the EGC. However, if there's only one wire exiting the enclosure, no need for a neutral conductor, and no place to attach one at the load, is it accurate to say there is no neutral conductor and that the single wire in question is the EGC?

    I apologize if this question seems obvious. The project is a unique mix of theory, terminology, codes, and best practices. I appreciate the help.

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Quote:

    if there's only one wire exiting the enclosure, no need for a neutral conductor, and no place to attach one at the load, is it accurate to say there is no neutral conductor and that the single wire in question is the EGC?

    There is no neutral then and you have the typical 3 phases and a safety ground.

    Keith Cress
    kcress - http://www.flaminsystems.com

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    (OP)
    That makes sense. Thanks again.

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Contact the power company and request a 120/208 Volt service, or a 120:240 Volt four wire open delta, or closed delta.
    You mentioned possible future expansion.
    It amy be well to provide a system with a neutral available.
    It may get expensive if you get a machine in the future that requires a neutral and none is available.
    Do not under any circumstance allow a Wye/Delta connected transformer.
    Wye/Wye, Delta/Wye, Delta/Delta are okay.

    Bill
    --------------------
    "Why not the best?"
    Jimmy Carter

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    (OP)
    I did not communicate with the power company in the early stages of this project, but my understanding is that 277/480 4-wire wye is the only option for us.

    The neighboring business had existing 3-wire delta service (not sure of the voltage) and they had to agree to accept this new service as part of our installation. The neighbors readily agreed, as they have experienced some equipment failures that were blamed on the 3-wire delta.

    "Expansion" for this particular facility would be realistically limited to one additional CNC machine. There simply isn't room or floor weight capacity for more or bigger machines. Buying an oversized transformer could support this one hypothetical additional CNC.

    Regarding Wye/Delta transformers, what is the concern? In my research, I've glossed over some comments centering on the topic, usually having to do with using a delta/wye transformer in reverse and whether or not to connect the primary neutral to anything. I didn't study further, as none of the transformers I've been shopping for have a wye primary. Perhaps that's a clue.

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Loss of a primary line can cause severe voltage crazyness on the delta side as it tries to 'correct' for the missing phase on the WYE side.

    Quote (waross)

    Phase loss on the primary causes backfeeds, circulating currents, overloads, burnouts, and/or blown fuses.

    Keith Cress
    kcress - http://www.flaminsystems.com

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    You may be aware that a small voltage unbalance in the supply to a three phase motor may cause a large increase in the motor current on one or more phases.
    An unbalanced voltage applied to a wye/delta transformer bank with the primary neutral connected causes a similar effect but often much more severe.
    If you float the primary neutral you may have damage caused by over voltage transients during primary switching.
    This is the short list of issues.
    The full list takes pages and pages.

    Bill
    --------------------
    "Why not the best?"
    Jimmy Carter

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    You must be sharing a transformer with other customers.
    120/208 Volts is a common, standard voltage across North America.
    Large apartment buildings, malls, large super markets, large schools, the list goes on of the normal applications of 120/208 Volts.

    Bill
    --------------------
    "Why not the best?"
    Jimmy Carter

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Quote:

    The neighbors readily agreed, as they have experienced some equipment failures that were blamed on the 3-wire delta.
    That is one of the possible issues with a wye/delta with a floating primary neutral.
    Utilities often use that connection because the issues become much worse if they connect the neutral.
    Generally found in very old legacy installations.

    Bill
    --------------------
    "Why not the best?"
    Jimmy Carter

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    (OP)
    Thanks again. This stuff is actually quite interesting.

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Power electronics do not like delta power sources. So for something like a CNC machine that will have 3 phase servo amplifiers and possibly VFDs for spindles, you want a wye secondary with a solidly grounded neutral. Your machine will not use the neutral so you would not need to run it out of the transformer, but you want that wye secondary. The only possibility of not needing it is if the machine mfr used 220V single phase input for all of the servo amps and VFDs by tapping two of the three phases, balancing out the current draw among the loads. Possible, but not probable. I only mention it because you seem to imply that this is a small machine.

    Common off the shelf distribution transformers will be 208Y120, but you can order one with a 240Y136V secondary if your machine can not tolerate the 208V input. Again, you will not use the L-N voltage so the fact that it would be 136V is irrelevant. This type of transformer configuration exists SOLELY for this purpose; supplying 230V machines that contain power electronics.

    The 480V primary of that transformer would be delta, even though your system is wye.

    If you CAN’T wait for that transformer and can’t use 208V, it is possible to use 240V delta, but you will have to get into your (3phase) servo amps and VFDs to ensure that the protective elements inside of them are not referenced to ground. Some NFPA privide simple ways to accomplish this by removing jumpers or screws, some require you to disassemble the units to get access to wires that need to be cut. Doing so sometimes voids the warranty, voids the UL listing (if any) but ALWAYS removes the protection features these devices provided. Do do at your own risk.


    " We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    If you must go delta, come back for a simple method of developing an artificial neutral or balanced grounding point.
    Three small lighting transformers will do it.

    Bill
    --------------------
    "Why not the best?"
    Jimmy Carter

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    (OP)
    Well, we have purchased a transformer: 75kVA Delta-Delta with center of one phase tapped.

    I hope it doesn't seem like I ignored the advice of some who gave reasons why a wye secondary might be better.

    We got lucky with a supplier right around the corner from our facility. Price and availability were appealing. After agonizing about it for far too long, I finally committed.

    Some additional points that the collective might find relevant:

    1. The machine has its own transformer inside. Could this be why the machine specs freely allow both delta and wye supply?
    2. Older documentation shows that the machine builder, Haas, has offered external transformers in the past for use in facilities with 480V service. These were Delta-Delta configured. (This is a separate, external transformer in addition to the internal, integral transformer.)

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Well, if life hands you a lemon, make lemonaid.
    On the positive side:
    1. You will have true 120:240 Volt single phase available if you need it.
    2. The center tap will provide a good grounding point. I would use the center tap for a ground before using an artificial neutral.
    3. Delta/delta avoids the problems seen with a wye delta transformer.

    BUT:
    Beware of jraef's advice.

    Quote (jraef)

    If you CAN’T wait for that transformer and can’t use 208V, it is possible to use 240V delta, but you will have to get into your (3phase) servo amps and VFDs to ensure that the protective elements inside of them are not referenced to ground. Some NFPA privide simple ways to accomplish this by removing jumpers or screws, some require you to disassemble the units to get access to wires that need to be cut. Doing so sometimes voids the warranty, voids the UL listing (if any) but ALWAYS removes the protection features these devices provided. Do do at your own risk.
    If you find that you need a symmetrical ground point come back for details on a "Roll your own" artificial neutral.
    If you use an artificial neutral you will not be able to use the center tap to supply 120 Volts.

    Bill
    --------------------
    "Why not the best?"
    Jimmy Carter

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Probably 80% of the Machine tools I service are fed delta or open delta. If they're older than a couple of years I've never seen one that needed the servo drives modified or checked. YES, I see lots and LOTs of new VFDs that scream check-or-I'll-die, because of newer built-in EMI mitigation. If it's a newer CNC certainly check the manual for allowed power connections. In the last couple of years, maybe eight or so, they've all started to include an entire chapter on power supply requirements. Very helpful actually. I suspect they know anything and everything can be out there for power and don't want unhappy customers or blown stuff to deal with and harming their reputations.


    The internal transformer you're talking about Nescius is not large is it? About the size of a basket ball give or take? You'd need one at least the size of the biggest motor to have it be a 'system transformer'. What you;re seeing is the "control transformer" which is there to run all the single phase equipment in the CNC machine. All the controls are usually 120Vac. The computers and PLCs etc. are 120 single phase powered and if the machine is fed 3Φ 240 or 480 then they need to transform that down and create a separately derived isolated single phase supply. Depending on which supply a machine gets fed the user/installer needs to confirm the taps are set on the control transformer for the circumstance.

    Thanks for coming back. Let us know how the rest of it goes.

    Keith Cress
    kcress - http://www.flaminsystems.com

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    (OP)
    Thanks, all.

    The plan is to bond the center tap to the equipment grounding conductor within the transformer enclosure. However, I will proceed armed with the above warning regarding differing line-to-ground voltages. I will ask Haas directly on this issue.

    itsmoked,

    The machine is new from the factory. Unfortunately, I have not seen it in person yet; it's waiting at the rigger's warehouse right now. My awareness of an internal transformer comes from what little installation documentation I could scrape together. Presently, my most detailed information is a document from 2011 and Haas has clearly stated that they do NOT provide instructions like that any longer. The 2011 document is mediocre, but adequate. The "new" information is a weak webpage with some bullet points and specs, no instructions.

    I need to put some pressure on Haas, or the factory outlet, to cough up the "real" documentation. They are obviously withholding it from us. Honestly, it's a bit disappointing.

    In any case, you could be right; the internal transformer might not do any heavy lifting, so to speak.

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Ideally you should use a Drive Isolation Transformer, 460 volts delta primary, 133Y230 volts secondary with the primary taps set at the HIGHEST voltage possible usually will be 5% Full Current Above Normal ( FCBN ) to bring down the secondary voltage to around 133Y230 volts. The Drive Isolation Transformers have the ability to handle harmonic currents from industrial rectifiers.

    Definitely solidly ground the secondary and then use 3 120 volt primary 12 volt secondary buck-boost transformers in the wye-wye autotransformer configuration to knock the voltage further down to 121Y210 volts. I am serious about this. A LOT of European solid state drive manufacturers such as Kollmorgen are under the FALSE impression that our industrial voltages are 127Y220 to 133Y230 volts and 254Y440 to 265Y460 volts like South American 60 cycle countries and Cuba have. If you expose a Kollmorgen 460 volt drive to 289Y500 or 300Y519 volts ( I have seen both on Cleveland Public Power at 5 AM in the morning during the summer ) a Kollmorgen drive will fry like bacon.


    After you put in that you can try changing the primary taps of the drive isolation transformer to 2.5% FCBN and see if that gives you around 220-225 volts and if so leave it there. Also, you should size the feeder and branch circuits to 140% of full load current to account for the matter that these drive very likely will be Periodic Duty not Continuous Duty. Also, National Electrical Code wire and circuit sizing is driven by the Cheaper-Than-Dirt-Cheap Club and going for a larger wire size and the largest fuses and circuit breakers will be prudent.

    Also, THWN/MTW wire only has a 60 degree Celsius rating when exposed to oil or gasoline not the 75 or 90 C rating that it has as building wire. A potential gotcha.

    Also apply whatever surge protection you can at the main distribution panel for the 277Y480 and on both sides of the drive isolation transformer. Do not skimp on this.

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    (OP)
    mc5w,

    Thank you for taking the time to reply. I must admit that some of what you wrote is over my head and I did unload the new transformer at the shop today, but I'm glad to learn more.

    I gather that a "drive isolation transformer" is designed to better withstand SCR loads that create unique demands on a transformer. As a layman with some hobbyist electronics experience, I can digest this in only a very basic way...current spikes associated with SCR switching and larger physical forces on the windings, perhaps?

    Then, is it a good thing that my plain vanilla transformer is greatly oversized, better able to endure the punishment of this type of duty? (75kVA transformer supplying a machine that can draw at most 28kVA continuously, and will usually draw only a fraction of that)

    Maybe it goes deeper than that and the DIT construction benefits the load as well?

    The machine specs give the acceptable voltage range as 195-260 Volts. The plan was to select primary taps that give an output voltage right in the middle of that range. I have no idea about the details of the electronics in our machine, but it sounds like you'd recommend we choose taps to minimize the output voltage.

    Surge protection is even more foreign to me than what we've been discussing so far. In this context, does "surge protection" mean devices to guard against lighting strikes?

    Thanks again.







    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    Go with the nominal voltage your machine requires. Your machine also will have NO Kollmorgen anything in it so you have nothing to fear there though that's good to know info.

    Keith Cress
    kcress - http://www.flaminsystems.com

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    You also need to install voltmeters so that you can monitor for when the power company jacks up their voltage during the summer so as to overcome undersized wiring in residential neighborhoods. For what your voltage range is 208 volts open circuit during the Winter would be prudent. You should also install an overvoltage relay that will sound an alarm or even cut power to the machine when the voltage exceeds 255 volts. An example was that about 1/2 or 1 hour after First Energy restored power on August 15, 2003 the open circuit voltage in Seven Hills was 125 volts. During the warm half of the year Cleveland Public Power jacks up the voltage on their 6,900Y12,000 volt system to more along the lines of 7,230Y12,500 volts so that people who are on 2,400 volt 3-wire 3-phase distribution will get more voltage for their air conditioners. At onbe place iun Cleveland supplied by CPP during the summer our service were reading 125/250 volts singlemnpohase and 289Y500 volts and in 1 service 300Y519 volts! Here in Columbus, Ohio American Electric Power's voltage inside my apartment reads 123-124 volts even though I live about 150 feet from the supply transformer in a 100 unit apartment building.

    You should also use antioxidant compound on copper wire that is formulated for use on copper wire. Ilsco Deox, Penn Union CuAl Gel, Burndy Penetrox E, and Thomas & Betts Kopr-Shield are examples. Deox and CuAl gel can be used to lubricate box lug setscrews but the latter 2 cannot because Penetrox E and Kopr-Shield contain colloidal copper to make them suitable for the threads of brass or bronze conduit and copper clad threaded sectional ground rods. One of the things the you WILL NOT find on the Consumer Product Safety Commission website was that when Dr. Jesse Aronstein was working on the Aluminum Wiring Failures Problem he tested copper-to-copper connection methods as a matter of scientific control to determine if it was the method or the material or both. These are the things that he determined:

    1. Copper oxide is just as much a fire hazard as aluminum oxide which was what the US Army Signal Corps was teaching their electrcians during World War 2. I have seen more in the way of copper wiring burn up than aluminum. I have used silicon carbide abrasive paper + elbow grease + Ilsco Deox electrical grease on the copper wiring for a replacement starter motor in a car. 3 years later I had to drop the starter motor and change the power relay. Ilsco Deox passed the 3 year salt spray test. Deox also caused the battery terminals to have ZERO sulfuric acid creep.

    2. You do indeed need to fan out all of the wire strands, cut off the sharp tips, clean each one with silicon carbide paper ) 220 or 240 grit for larger wire sizes and aluminum, coat them with electrical grease, and recompress with a hose clamp. When I was a 3 year old grandfather taught me how to bunch clean the wire strands of lamp cords and extension cords with diagonal cutters which works for wires #10 AWG or smaller with 19 or more wire strands.

    3. Other methods of connecting stranded copper wire that most people use only have vhave the outside layer of wire strands conducting even if the circuit is direct current. The Ericson company in Willoughby, Ohio determined that when most people make a crimped or box lug connection to copper wire they only have the outside wire strands conducting. This issue is why long before Dr. Aronstein was born Erico invented exothermic welding of copper wire. Burndy has told me at a trade show that some of their customers have built heat sinks for welding Burndyweld lugs to insulated building wire.

    4. A steel wire brush is 100# INEFFECTIVE at removing aluminum oxide and that Burndy Penetrox is also 100% ineffective at penetrating aluminum oxide. What you need to remove aluminum oxide are either #220 or #240 grit silicon carbide abrasive paper or a tungsten inert gas welder. I demonstrated when using 4-wire aluminum service entrance cable to hook up a plastics machine with 60,000 watts of electric heaters in it that you can sand each wire strand dry and then put Deox on it right away. I have told Dr. Aronstein by email and the telephone that you do not have to grease the wire strands and then clean them. There are also a few other issues such as cutting off the sharp tips of the strands before cleaning them and deliberately overstripping the insulation so as to have a strand bending area in order to fan them out. Use a 1/4 inch screwdriver shaft to maintain a minimum bending radius of the strands. I still have not figured out who to degrease my hands frequently without using perchloroethylene brake cleaning spray. Next time I go to a trade show I will go to the industrial hygiene booths first and see what solutions they have. If you a solution for degreasing my hands please let me know. Also, for compact stranded wire cleaning the concave surface of the wire strands and the other 3 sides is essential to interstrand conduction and having all wire strands conducting regardless of whether it is copper or aluminum. Yes, there is compact stranded aluminum.

    I know this sounds like a lot of extra work but for how much coipper wire and aluminum wire costs these days would the customer want half the wire strands conducting of all of them conducting?

    You can contact Dr. Jesse Artonstein at protune@aol.com .

    RE: Assistance choosing a 3-phase transformer to supply a CNC machine

    There are probably a few million copper wire connections made each year without any cleaning whatsoever that stand the test of time.
    However if you have the misfortune to work with stranded wire that has been exposed to the weather for a long time, then cleaning is a very good idea.
    At times I have encountered copper wire with corroded strands. I have often been able to trim a few inches or more off the end of the cable and find clean copper. Sometimes this is not possible and I have to clean the strands.
    The worst case of copper corrosion that I have seen was a bad connection on a DC press motor.
    The bad connection heat cycled and caused enough copper oxide to form that the connection acted as a copper-oxide rectifier. The motor would run forward but not in reverse.
    Aluminum oxide is difficult to see and unless removed within the preceding few minutes is always there on unprotected aluminum.
    Copper oxide is visible and distinctive. Clean copper is no problem
    Anyone who connects discoloured copper without cleaning it first gets what they deserve.

    Bill
    --------------------
    "Why not the best?"
    Jimmy Carter

    Red Flag This Post

    Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

    Red Flag Submitted

    Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
    The Eng-Tips staff will check this out and take appropriate action.

    Reply To This Thread

    Posting in the Eng-Tips forums is a member-only feature.

    Click Here to join Eng-Tips and talk with other members! Already a Member? Login


    Resources


    Close Box

    Join Eng-Tips® Today!

    Join your peers on the Internet's largest technical engineering professional community.
    It's easy to join and it's free.

    Here's Why Members Love Eng-Tips Forums:

    Register now while it's still free!

    Already a member? Close this window and log in.

    Join Us             Close