Cantilevered timber poles supporting timber Deck

Cantilevered timber poles supporting timber Deck

Cantilevered timber poles supporting timber Deck

(OP)
Hi All,

Really simple query,what deflection limit would you use when designing cantilevered timber poles supporting a timber deck. As the decks as sitting on posts / poles (2.4-3m high), they may be some apparent sensory vibration.

Traditionally, the 'codes' [Aus/NZ] here do not give any guidance and thus there appears to be a bit of finger licking? I would check serviceable loads against a height/250.

Does anybody have any references for deflection limits or any comments?

Cheers

RE: Cantilevered timber poles supporting timber Deck

You might Google Frank Woeste. If anybody's studied this, it's surely him. I think h/250 seems reasonable but that's just instinct talking.

HELP! I'd like your help with a thread that I was forced to move to the business issues section where it will surely be seen by next to nobody that matters to me: http://www.eng-tips.com/viewthread.cfm?qid=456235

RE: Cantilevered timber poles supporting timber Deck

As a minimum, height/300 for sway. However, this results in 10mm sway... Sitting on that deck with a pina colada will be like sitting on a cruise ship.. And that’s before creep kicks in.

Can’t you brace it?

RE: Cantilevered timber poles supporting timber Deck

It's not the deflection limit that gets you it's what horizontal load you use to generate the deflection, In the UK we have a horizontal load based in a proportion of dead and live load as a minimum horizontal load (great for buildings) but this has been found to be to small for mezzanines and there is specific guidance for such structures (if wind loads are applied these would generally govern). As for a limit H/300

RE: Cantilevered timber poles supporting timber Deck

(OP)
Thank you for the advice. H/250-300 or 10mm seems reasonable I guess.

MIStruct_IRE - The Deck cannot be braced underneath, however I have strapped it back to the floor of the house which should really take any vibration out of the floor / posts.

Countervail / KootK - thank you for your comments.

RE: Cantilevered timber poles supporting timber Deck

Check people if people can get it moving back and forth too.

You don’t want some kids seeing how far they can get it moving.

RE: Cantilevered timber poles supporting timber Deck

Quote (countervail)

n the UK we have a horizontal load based in a proportion of dead and live load as a minimum

Out of curiosity, what percentage is used for this?

HELP! I'd like your help with a thread that I was forced to move to the business issues section where it will surely be seen by next to nobody that matters to me: http://www.eng-tips.com/viewthread.cfm?qid=456235

RE: Cantilevered timber poles supporting timber Deck

You can also diagonally brace just under the decking or underside of the Joists with some strap braces corner to corner. This may ensure you are at least trying to engage all posts against any sidesway, rather than perhaps engaging a single line since any decking is a pretty poor diaphragm.

I've been in a number of houses supported on poles of dubious construction with no subfloor bracing down to ground and they do tend to move a fair bit, over time it tends to get worse as connections in timber framing lossen up in the subfloor. Depending on location you are in the house, you can get all sorts of weird effects like feeling someone walking down the other end of the house being felt.

I feel in these things that it's prudent to provide some forewarning to the client that it's possible given the type of construction with no bracing, and height of the poles that they may perceive some vibration/movement, and if it's noticible there may be things you can do to lessen the perceived vibrations after the fact so they know they have options. They may have different expectations after all that it will be totally rigid or something.

RE: Cantilevered timber poles supporting timber Deck

If you have strapped the deck to the house, it now becomes a anchored diaphragm. If you are in a seismic zone, you should check the capacity of the ties versus whatever the diaphragm weight with the seismic factor. The deck should also be attached to the house at the face of whatever house framing you have to take the horizontal shear at that connection. Actually now, you don't care how high your poles are because the house is resisting the full lateral loads. You just have to make sure that the diaphragm has stiffness with plywood or metal cross straps under the deck. If you just have timber planks for flooring, there can be some movement. Very common design in California.

RE: Cantilevered timber poles supporting timber Deck

Indeed.

is this deck attached to a structure?

RE: Cantilevered timber poles supporting timber Deck

Quote (KootK)

Quote (countervail)


In the UK we have a horizontal load based in a proportion of dead and live load as a minimum
Out of curiosity, what percentage is used for this?

I'm also curious. In construction platforms, 2% is a common rule of thumb. (Actually, it's probably codified in ASCE 37 now).

----
just call me Lo.

RE: Cantilevered timber poles supporting timber Deck

Review micks87 9 Aug 23:07 post -"however I have strapped it back to the floor of the house which should really take any vibration out of the floor / posts."

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Research Report - What’s the State of Nonlinear Simulation?
Simulation is an increasingly valuable tool across the product design workflow, but not all simulations are equal. We set out to determine how engineers and product designers make use of specialized analyses, how they incorporate nonlinear simulation into their work and how they rate the available software. Download Now
White Paper – Data Security and Know-How Protection
Our data is constantly exposed to the danger of being intercepted or stolen as it wends its way over global data networks. Data security measures and measures for protecting intellectual property should not, however, first be implemented when data is exchanged – companies must lay the foundation for these measures within their own organization. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close