30+ year old Current Transformers

30+ year old Current Transformers

30+ year old Current Transformers

(OP)
I have a project to update power metering in a building. The existing CT's and PT's are 0.3% and would meet project requirements for accuracy but they are over 30 year old. In your opinion do CT's and PT's accuracy degrade over time. Thanks

RE: 30+ year old Current Transformers

Quote (Measuring the dissipation/power factor (tan(δ) delta) allows you to determine the condition of the insulation. When you use our testing systems, you will also be able to determine the dissipation factor at various frequencies and detect any signs of aging at an early stage.)


The IEEE Std C57.13 provide guidance to test instrument transformer for performance measurement and accuracy. A dielectric test such as the dissipation factor is available. It provides a diagnostic of an aging process taking place (moisture ingress, partial discharge, etc).

After 30 years in service most likely the Instrument transformer are in the wear-out region of the typical bathtub reliability curve were the risk of failure rate increase continuously. compromising system reliability.

Few strategies have been used to mitigate the risk of failure of re-using an old unit. Often ordering spare unit is only justifiable if the cost and consequences of a power failure can be tolerated. Otherwise, replacing 30 years old equipment may be a reasonable option.

RE: 30+ year old Current Transformers

Just as power transformer losses will not increase with time, accuracy of CTs should not deteriorate with time. Of course if the steel starts rusting, it may due to higher exciting current.

RE: 30+ year old Current Transformers

I suppose the insulation could degrade, especially the winding insulation of a PT, which could mean it is more susceptible to complete failure. But I wouldn't expect the accuracy to degrade.

RE: 30+ year old Current Transformers

I haven't yet seen a failure of a window-type CT that wasn't abused - exposed to weather, high temperatures, open-circuited, etc., in the thirty-odd years I've played with them in metal-clad gear.

Same goes for those mounted internally in transformers and oil circuit breakers.

Of course, getting wet, subjected to high temperatures, proximity to faults (fire, blast debris) negate that 'wasn't abused' caveat.

old field guy

RE: 30+ year old Current Transformers

Below is a sample of a CT failure after testing.

RE: 30+ year old Current Transformers

I would expect that the insulation - both solid and paper has degradation issues. What is the company's standards for when they take these kind of transformers out of service?

RE: 30+ year old Current Transformers



We have found several older ABB/ITE CT's completely break down under normal conditions, summer heat but still normal

RE: 30+ year old Current Transformers

Thermoplastics that melt are rarely used in electrical areas where heat can be high. This is probably a case where some thermoset plastic was not properly catalyzed and therefore never fully hardened. I've come across that a couple times in my life.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - PLM and ERP: Their Respective Roles in Modern Manufacturing
Leading manufacturers are aligning their people, processes, and tools from initial product ideation through to field service. They do so by providing access to product and enterprise data in the context of each person’s domain expertise. However, it can be complicated and costly to unite engineering with the factory and supply chain. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close