Interpretation of OSHA standard about diked area for flammable liquid storage

Interpretation of OSHA standard about diked area for flammable liquid storage

Interpretation of OSHA standard about diked area for flammable liquid storage

(OP)
I have trouble understanding this part of OSHA's code about dikes:

1910.106(b)(2)(vii)(c)(1)
Except as provided in subdivision (2) of this subdivision, the volumetric capacity of the diked area shall not be less than the greatest amount of liquid that can be released from the largest tank within the diked area, assuming a full tank. The capacity of the diked area enclosing more than one tank shall be calculated by deducting the volume of the tanks other than the largest tank below the height of the dike.

Does this mean that dikes containing more than one tank should be shorter?

RE: Interpretation of OSHA standard about diked area for flammable liquid storage

It means the volume of the diked area has to account for any volume displaced by the tanks other than the one under consideration (the biggest one).

If a tank other than the one under consideration has its bottom below the top of the dike, the volume of the dike still has to be enough to contain the volume of the biggest tank.

RE: Interpretation of OSHA standard about diked area for flammable liquid storage

(OP)
Okay, thanks! that makes a heckuva lot more sense!

RE: Interpretation of OSHA standard about diked area for flammable liquid storage

NFPA-30 says the same thing, perhaps in a more readable way.
SPCC requires you to account for a rain event in your dike volume.
Accordingly, a "rule of thumb" has been used to have the dike volume 110% of the largest tank volume.
I've seen where local jurisdictions require enough dike volume be available to also contain a 24 hour 100-year rain event, sometimes with an additional cushion.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close