Hi all,

Something weird is happening to this generator. It is driven by VFD that is connected via DC-bus to a another inverter that supplies the power to grid. At some point Voltage and current supplied to grid starts to oscillate. Does anyone have a idea what could be causing this behavior? See attached picture.

Trends from top to bottom:

Generator voltage AC
Grid voltage AC
Grid converter DC
Grid current
Grid power (Kw)

RE: Permanent magnet generator question

Hi Teppo, welcome to Eng-Tips.

I'm a bit confused because I've never heard of a GENERATOR being driven by a VFD. VFDs usually drive motors.

Is the VFD actually driving a motor that is then turning a generator?

Keith Cress
kcress - http://www.flaminsystems.com

RE: Permanent magnet generator question

(OP)
Hi,

No, generator is started as motor and then "switched" to generator by applying external moment to rotor. It's high a speed machine and the the generator nominal is frequency about 1700Hz, so for obvious reasons it cannot be driven without VFD.

RE: Permanent magnet generator question

Hi Teppo,
1. could you give more informations about lines of the graphs?
2. Normally when lot of signal is missing some protection system is activated and the control change in "safety protection" mode. in this case before and after problem you have no particular change and this give me indications that problems is in the measurements chain only
3.Could you paste indications about connections

Regards

RE: Permanent magnet generator question

(OP)
Hi,

1. Not much, i'm not currently at site myself. The drops at about 1/3 from left on the graphs are normal shutdown procedure. the problem starts at about center of the trends. Time interval of trends is 24h. Data is read via bus to the control system and i really don't know is it manipulated/filtered etc. or how it is calculated by VFD.

Trends from top to bottom:

Generator voltage AC
Grid voltage AC
Grid converter DC
Grid current
Grid power (Kw)(- means to the grid)

2. yes it might be problem only in the measurement chain.

3. Sorry i don't understand the question.

RE: Permanent magnet generator question

What is your prime mover?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Permanent magnet generator question

It looks as if your generator voltage is a straight clean line.
The grid voltage is all over the place.
That is a lot of grid upset to be caused by a tiny 15 kW generator.
How about the whole picture?
What is driving the generator?
What type of loads are on the grid?
From the little information given we can only give WAGs. (Wild ASSumptive Guesses)

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Permanent magnet generator question

(OP)
Hi,

i don't have much more to work with.

Generator is connected straight to a substation (20kV >400V). I guess substation is about 1000kVA or more. I don't know what kinds of other loads are connected to same substation, but mostly motors i think. It's industrial site so there should be compensation batteries for reactive power.
The problem seems to start at random intervals and doesn't stop before restart.

RE: Permanent magnet generator question

There is a sharp step down, then back up which occurs about 1/3 of the distance along the time axis.
Does that have a known cause (in which case please tell us what's going on there), or is it part of the unknown behavior you are trying to explain?

=====================================
(2B)+(2B)' ?

RE: Permanent magnet generator question

Quote (Teppo (OP))

The drops at about 1/3 from left on the graphs are normal shutdown procedure. the problem starts at about center of the trends.
Teppo, you list five parameters but i can't identify 5 traces on your attachment.
Your output may be causing an interaction with an On-Load-Tap-Changer.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Permanent magnet generator question

(OP)
Hi,

First trace is very easy to miss, because it is so linear, but it's there. As Waross pointed out the drop at 1/3 from the left is normal.

RE: Permanent magnet generator question

(OP)
Hi,

Here On-Line-Tap-Changers are installed at 110 kv grid, however it can still be the cause of the voltage drop. Grid is something like this 400kv > 220kv > 110kv > 20kv > 400V.

RE: Permanent magnet generator question

I read the trend as about 14 kW output. Is this correct?
Is the substation owned by the utility or by the client?
What powers the generator?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Permanent magnet generator question

(OP)
Hi,

I guess substation is owned by the client. 14kw is correct. Prime mover is a gas turbine powered by biogas.

RE: Permanent magnet generator question

First I would as soon as possible check the tap changer. It may be fine, but if it is switching between tap positions so rapidly as to cause those traces, it may not last long.
I suggest to first rue out the tap changer as the source of the problem and then move on to other possible causes.
Is it possible to get a trend of the grid voltage when the generator is NOT online?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Permanent magnet generator question

Quote (electricpete)

There is a sharp step down, then back up which occurs about 1/3 of the distance along the time axis.
Does that have a known cause (in which case please tell us what's going on there), or is it part of the unknown behavior you are trying to explain?
Would you mind answering my question please? Thanks.

=====================================
(2B)+(2B)' ?

RE: Permanent magnet generator question

Pete:

Quote (WARoss)

Quote (Teppo (OP))
The drops at about 1/3 from left on the graphs are normal shutdown procedure. the problem starts at about center of the trends.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper – Data Security and Know-How Protection
Our data is constantly exposed to the danger of being intercepted or stolen as it wends its way over global data networks. Data security measures and measures for protecting intellectual property should not, however, first be implemented when data is exchanged – companies must lay the foundation for these measures within their own organization. Download Now
White Paper – Collaboration in the PLM Context
The influence exerted by the Internet of Things (IoT) means that there is a steadily growing need for collaboration in industry. Partners from new industries and areas of application need to be integrated in cross-company business processes to ensure that the lifecycle of smart, connected products can be managed from end to end. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close