AS1170.2 Local pressure questions

AS1170.2 Local pressure questions

AS1170.2 Local pressure questions

(OP)
A couple of questions about Kl local pressure factors:

1. Do you use them for serviceability calculations?

2. Where there are two contributing external surfaces (e.g. top and bottom surfaces at eaves), do you apply Kl simultaneously to both surfaces?

RE: AS1170.2 Local pressure questions

1. Yes most definitely. The higher pressures are a function/characteristic of the airflow around the building, and for the most part are independant of the wind speed whether at ULS or SLS.

2. I think this aspect is less clear, but taking a page out of the part in code related to canopies it's applied once to the total net pressure calculated. Which I guess is the same as stating its applied to both surfaces.

RE: AS1170.2 Local pressure questions

(OP)
1. What purlin deflection limits do you recommend for localised serviceability pressures?

2. Yes I multiply the whole thing, as it’s simpler and conservative. I was wondering though if there was a clause somewhere which says you needn’t bother, since it doesn’t really make sense to be adding up local pressures across multiple surfaces.

RE: AS1170.2 Local pressure questions

Same deflection limits as normal areas. Why should there be any relaxation if that's what you are angling for. It's a deflection under a design load, the limit should not be dependant on the level of that load if you like. They are independant things.

RE: AS1170.2 Local pressure questions

(OP)
I meant what is a normal cladding/purlin deflection limit for serviceability wind speeds (inclusive of local pressure factors). L/150* seems to be a very common number. It's in all the purlin tables.


*Obviously you can tighten this up if you're supporting something brittle, or hanging a ceiling, etc.

RE: AS1170.2 Local pressure questions

Is it wrong to have a local pressure increase on two surfaces? My one book on wind loading didn't give me an answer. As1170.2 clause 5.4.3 does however rule out the combination factor (multi-surface reduction) for cladding and purlins.

RE: AS1170.2 Local pressure questions

(OP)
Steveh49, That Kc limitation was in AS1170-2002 but I can't see it in the current version? Which version are you looking at?

RE: AS1170.2 Local pressure questions

Span/150 seems to be used around here unless you have a ceiling then span/300 - span/360 seems to be the norm.

Keep in mind the local pressure can only have a 1:4 ratio for applying it on a span, so for longer spans it's only applied over part of the span assuming purlin spaced at 0.9-1.2m which seems to be the norm if there is a ceiling.

I'd say in the current version Kc would be 0.9 for internal and external coefficients for purlin design if there are two effective surfaces. To qualify it implies both internal and external pressures acting in the same direction, otherwise its 1.0. Refer to cases E & F in table 5.5

RE: AS1170.2 Local pressure questions

It was the 2002 version + A1 because I could download it from Parks Vic while using phone. Thought it was still current but maybe it's 1170.0 that's still from 2002 plus amendments.

RE: AS1170.2 Local pressure questions

(OP)
The As1170.2-2011 Kc clause is different to 2002. It’s more rational in 2011 version. Kc is presented more purely in terms of the number of effective external surfaces that contribute to an action, as opposed to specific prescribed combinations of external surfaces.

Under 2011 I would read it that you can apply Kc=0.9 to the top and bottom surfaces of eaves purlin.

RE: AS1170.2 Local pressure questions

I agree with that but still curious whether the local increase is transient and possibly non-additive or a 'permanent' function of the geometry.

RE: AS1170.2 Local pressure questions

(OP)
My opinion is that it doesn’t make sense to add local pressure factors across multiple surfaces, given that the whole point of local factors is they are transient isolated loads akin to point loads, but that the way the code is written and interpreted you probably should add them anyway.

RE: AS1170.2 Local pressure questions

One way you could potentially argue less would be to apply the windward wall K_l of 1.25 (or more if near the corners) to the underside of the windward overhang as this is where the pressure load under is coming from, and a K_l of whatever would normally be on the roof on top. Kind of makes sense to me but then you have to argue a possible deviation from the literal interpretation of the code.

RE: AS1170.2 Local pressure questions

(OP)

Quote (agent666)

One way you could potentially argue less would be to apply the windward wall K_l of 1.25 (or more if near the corners) to the underside of the windward overhang as this is where the pressure load under is coming from, and a K_l of whatever would normally be on the roof on top. Kind of makes sense to me but then you have to argue a possible deviation from the literal interpretation of the code.

I would have thought that would be a literal interpretation, given that the code says to apply the wall pressures to the underside of eaves?

ps: windward wall local pressures are now 1.5, not 1.25

RE: AS1170.2 Local pressure questions

Yeah agree totally with what you say.

Somehow when writing it I had canopies on the brain and the fact they calculate out to a single pressure coeff inclusive of equivalent internal/external pressures to which you then apply a single K_l factor presumably based on the roof (not part wall part roof). So was arguing you might be able to reduce it based on the underside pressure coming from the wall like you note.



Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close