Now I'm going to assume National Building code, based on the fact you appear to be out of BC.
I believe the 2015 code allows you to not account for roof live and snow acting simultaneously, however if you have a beam supporting second floor and roof loads, then you would need to account for them concurrently.
Forte doesn't know whether you have pt in roof live load, or floor live load, and therefore must use your inputs, and the code prescribed load combinations. If you only have roof live and snow, then you need to run the beam separately, one with the roof live, and the other with the snow.