×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Ht motor

Ht motor

Ht motor

(OP)
Hello sir we have ht 1250kw ht motor this motor is windede so we take that motor empty trial load is 40 amps.but motor temperature is starting in empty motor 60°c and humming sound come why motor getting temperature and humming sound please tell Maine proper rieson

RE: Ht motor

Loud sounds, leaking water and low flow rate are all common Pool Pump Issues.

RE: Ht motor

You haven't mentioned the Voltage the motor runs at, however it appears to be a 6600 Volt rated Motor for which the No Load Amps of 40 appears to be about right. The temperature could be caused by shorted laminations in the Stator core as there is no load to cause any temperature rise in the Windings. The humming sound could be due to many reasons from a loose core (Stator or rotor) to unbalanced Air Gap, a wrong Winding connection, unbalanced Voltage, broken rotor bars/rings to name a few, it could also be a combination of these.

RE: Ht motor

Do I understand that this motor was rewound? Possibly one or more coil groups have been reversed.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Ht motor

What does 60C represent? winding temperature by RTD? Bearing temperature?

Have you double checked the temperature measurement (consideration of RTD type, possible loose connections....).

What is the ambient temperature?

Have you verified the voltage supplied to the motor is balanced and correct?

How many leads are brought out to the terminal box? (If it is 6 and you reverse one pair of line and neutral leads, you can expect some problems.)

Was the motor run by the rewinder? Do they have test results?

How long was the run, and was a steady trend value seen? Although I normally see continuous increasing trend in temperature, it seems possible winding temperature might peak shortly after uncoupled start (due to starting current) and then decrease.


=====================================
(2B)+(2B)' ?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources

eBook – How to Choose the Correct Corrosion Testing Method
When designing a metal component, engineers have to consider how susceptible certain alloys are to corrosion in the final product’s operating environment. In a recent study by NACE (National Association of Corrosion Engineers), it was estimated that the direct and indirect costs of corrosion in the United States is approximately 6.2% of the GDP. In 2016, that cost exceeded $1 trillion dollars for the first time. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close