VFD cable and compression lugs
4

VFD cable and compression lugs

VFD cable and compression lugs

(OP)
Is VFD cable requiring special compression lugs?

In our application we are using 500 MCM VFD cable, Lutze A2205003.

Link

We intended to use compression lugs 500 MCM compression lugs, Punduit LCA500-1-6 with this cable:

Link

However, when conductor is stripped from isolation fine strands fan out and won't fit inside of compression lug. Are there special compression lugs required for fine strand conductors? Maybe there are some tricks how to make it fit. Please, share your experience.

PaulBr.

RE: VFD cable and compression lugs

3800 strands? I doubt that you will get that into a 500 MCM lug.
I fought with locomotive cables. Much less than 3800 strands but similar flaring.
I used a small Aero type hose clamp to contain the strands.
I left about 1/8 inch of the strands protruding to start into the lug.
Once the strands were started into the lug, the hose clamp was loosened slightly so that the lug could be tapped further onto the cable.
Then the hose clamp was removed and the lug tapped all the way onto the cable.
But:
I was using set screw type lugs.
I needed to use an oversized lug.
If you have to use a 750 MCM lug you will have approvals issues compressing it with a 500 MCM die.
Suggestions:
Ask Lutze for recommendations for lugs.
or
Go to set screw type lugs.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: VFD cable and compression lugs

Yes, there are special lugs AND DIES for what is referred to as “Class K stranding” of conductors. You cannot use standard compression lugs or dies. The cable mfr would have done you a favor to mention that in their specifications, I guess they don’t care....


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

RE: VFD cable and compression lugs

3
Here is a nice discussion in general using mechanical lugs on flex wire,
https://lugsdirect.com/GuideToFlexFlexibleFineStra...

Here is one source for properly rated compression lugs,
https://www.morrisproducts.com/pc_product_detail.a...

And from Panduit,
http://www.panduit.com/heiler/CatalogCutSheets/D-P...

The proper lugs and info are out there, but there are still some gray areas, like for Class K wire, if it is listed as "Class K "flex" wire" instead of Class K MTW/welding wire/battery wire then technically it is only permitted by "specific additional testing". Take a quick look here,
https://lugsdirect.com/UL486%20&%20CSA%20C22.2...

When dealing with fine strand cable I start to strip off the insulation, move it away for the cable far enough to use a tie wrap around the strands, then as I remove the insulation I keep pushing the tie wrap up close to the end, insert the cable in the lug, then as the cable goes in I cut the tie wrap, goes fast and other than wasting a few tie wraps, has worked well for me over the years.

Hope that helps, MikeL.

RE: VFD cable and compression lugs

(OP)
Thank you all for the info. Something to study.

PaulBr.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Research Report - How Engineers are Using Remote Access
Remote access enables engineers to work from anywhere provided they have an internet connection. We surveyed our audience of engineers, designers and product managers to learn how they use remote access within their organizations. We wanted to know which industries have adopted remote access, which software they are using, and what features matter most. Download Now
eBook - Managing the Context of Product Complexity Using the Digital Twin
Keeping track of changes to complex products is difficult—think Aerospace & Defense equipment, new generations of commercial aircraft, and software-based automobiles. A new way to managing the digital context of the physical product is required and the answer is the Digital Twin. This ebook explores the opportunity available for Operations and Maintenance for the Digital Twin. Download Now
White Paper - Trends in Industrial Filtration
Substantial progress has been made in filtration technologies in recent years. New filter media materials, designs and processes have led to filters that are more efficient, reliable, compact and longer lasting. This white paper will discuss the various trends that are impacting operational responsibilities of MROs today and the resources that are available for staying up-to-date on the latest filtration solutions. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close