not a disaster (yet), but certainly a rework failure
2

not a disaster (yet), but certainly a rework failure

not a disaster (yet), but certainly a rework failure

(OP)
Clemson University student apartments at 114 Earle which opened in August 2017 has experienced first floor concrete cracking and settlement.


Apparently they attempted to repair the cracks via expanding foam. However the crack seem to have effected more than just the floor. It looks like the sewer system may have been compromised also.

scroll down
down
down




down


down



down






down




keep going











Oooopsy
Replies continue below

Recommended for you

RE: not a disaster (yet), but certainly a rework failure

Hahahah. That's amazing; talk about making a bad problem worse.

Ian Riley, PE, SE
Professional Engineer (ME, NH, VT, CT, MA, FL) Structural Engineer (IL, HI)
American Concrete Industries https://americanconcrete.com/

RE: not a disaster (yet), but certainly a rework failure

And Clemson is an Engineering school ...

I think we need to put a hold on hiring from them.

----------------------------------------

The Help for this program was created in Windows Help format, which depends on a feature that isn't included in this version of Windows.

RE: not a disaster (yet), but certainly a rework failure

Whoever was doing the deep-injection foam (Uretek?) probably feels pretty stupid about now...

RE: not a disaster (yet), but certainly a rework failure

What's the removal process for expanding foam in an inaccessible area like the plumbing? I've never found a solvent that worked to remove solidified expanding foam. Methylene chloride? MEK?

Ian Riley, PE, SE
Professional Engineer (ME, NH, VT, CT, MA, FL) Structural Engineer (IL, HI)
American Concrete Industries https://americanconcrete.com/

RE: not a disaster (yet), but certainly a rework failure

Assuming PVC piping was used, there's likely nothing that will work on the foam that won't dissolve the pipes also. Most likely all of that sewer line will have to be replaced or abandoned, and new lines run.

RE: not a disaster (yet), but certainly a rework failure

A roto-rooter will do it.

RE: not a disaster (yet), but certainly a rework failure

Foam guys probably were paid by the cubic yard injected. However let's wait for an engineering report by a non-university company.

RE: not a disaster (yet), but certainly a rework failure

A look at google street view and the History (street view) shows a lot of soil work, spread out over time, during the course of construction.



Larger Photos:
Link
Link
Link

RE: not a disaster (yet), but certainly a rework failure

Um, must of hired a bunch of freshman engineering students . . .

RE: not a disaster (yet), but certainly a rework failure

Roto-Rooter might be able to mechanically remove some or most of the foam, but the inside of the pipes are going to be rough as a cob and will create nothing but problems in the future. Vents would need to be done, as well. Best bet is to tear out and replace.

It is better to have enough ideas for some of them to be wrong, than to be always right by having no ideas at all.

RE: not a disaster (yet), but certainly a rework failure

Somewhere the foam had to get into the lines, which means there's at least one hole in the sewer line. If it's similar to the system we've specified in the past, the injection probe had to have broken into the sewer line and the pressure near the injection site likely burst a significant length of the line.

RE: not a disaster (yet), but certainly a rework failure

...or perhaps a broken sewer line and loss of soil explains the original cracking and settlement of the slab.

RE: not a disaster (yet), but certainly a rework failure

This looks like a job for the worlds smallest tunnel boring machine.

RE: not a disaster (yet), but certainly a rework failure

I'm confused. Isn't the concrete part of the structure's.. support? How do you fix concrete cracks with some foam, especially cracks so big foam is even considered as some sort of wholesale jumbo crack-filler?

Keith Cress
kcress - http://www.flaminsystems.com

RE: not a disaster (yet), but certainly a rework failure

Keith,
I think the foam would have been intended to arrest settlement, not fix cracks in the concrete. The cracks could have partly been the result of the settlement.

This is going to involve some substantial demolition. I would start at that toilet, especially if it is the only one. The broken plumbing line/connection hopefully is not far away.

RE: not a disaster (yet), but certainly a rework failure

2
All I have to say, having gotten some of that stuff on my fingers before, is thank god someone wasn't on the can when that stuff erupted flush

RE: not a disaster (yet), but certainly a rework failure

How much additional concrete cracking was "caused" by the expanding foam in confined spaces?

RE: not a disaster (yet), but certainly a rework failure

I see Hokie. I was thinking multi-floor kind of situation. Thanks.

I knew a guy who's entire business was pumping concrete under foundations to completely re-level them and the structures on top of them. Worked great and he made an absolute killing at it.

Keith Cress
kcress - http://www.flaminsystems.com

RE: not a disaster (yet), but certainly a rework failure

"I knew a guy who's entire business was pumping concrete under foundations to completely re-level them..."

The foam is similar, but when done by an experienced crew, can actually be more accurate. It can also be used to restore (lift) building foundations. For that, the foam is injected into the soil around and below the perimeter of the foundation to solidify the surrounding soil, then the area directly under the foundation is injected to lift the foundation. It's pretty impressive, and it only takes a few hours.

RE: not a disaster (yet), but certainly a rework failure

Polyurethane foam mudjacking has been used in our neck of the woods for quite some time as well, with very good results. The permanency of the stuff is impressive, as long as it's not exposed to UV, as someone else mentioned. It's a real bugger to remove after errant placement.

It is better to have enough ideas for some of them to be wrong, than to be always right by having no ideas at all.

RE: not a disaster (yet), but certainly a rework failure

Urethane foams cure by reaction with moisture, which is why they are noted as being very difficult to remove from wood or skin (both contain plenty of moisture).

RE: not a disaster (yet), but certainly a rework failure

Yep Compositepro, it's like injecting a really large quantity of Gorilla Glue into the ground...

RE: not a disaster (yet), but certainly a rework failure

I'm surprised by the foam angle as anyone who's tried to mix some polyurethane to fill a space 'just so' usually misses by a chagrined mile. To inject something then 'have it expand' and to end up with 'accuracy' used in the same sentence... I just learned something.

I still envision polyurethane turning dark brown and changing to dust in a decade.

Keith Cress
kcress - http://www.flaminsystems.com

RE: not a disaster (yet), but certainly a rework failure

Apparently, the guys at Uretek are a bit better at getting that foam 'just so' - they routinely jack slabs to within an 1/8" of their target position. Of course, underneath, it doesn't have to be any particular shape or fit within a confined area.

RE: not a disaster (yet), but certainly a rework failure

They are using a two component material that is more predictable in terms of how much expansion and cell size is generated.

RE: not a disaster (yet), but certainly a rework failure

Yeah epoxybot, that certainly helps. There's alot of science behind it, but the guys who do the deep injection stuff to lift slabs and foundations are still artists in my book.

RE: not a disaster (yet), but certainly a rework failure

I didn't realize that e-pox. Thanks for that bit of education.

Keith Cress
kcress - http://www.flaminsystems.com

RE: not a disaster (yet), but certainly a rework failure

Imagine if somebody had happened to have been 'on the throne' during that foam eruption...

RE: not a disaster (yet), but certainly a rework failure

I imagine they'd have had to visit the 'pox doctor.

A.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close