Conversion of VGO (70 Deg C) storage cone tank to 140 Deg C VGO tank.
Conversion of VGO (70 Deg C) storage cone tank to 140 Deg C VGO tank.
(OP)
Sirs,
We are having an insulated cone roof tank which is storing VGO at temperature of 80 Deg C. Now we are urgently required to store VGO at an elevated temperature of 150 Deg C with out modifying the existing tank. we also checked the tank shell plates thickness at this elevated temperature and found OK.The tank is designed for 90 deg C as per code API 650.But for higher temperature API 650 Appendix M is applicable.
My question is
What are the precautions to be taken for the existing tank to store VGO at 150 deg C?.
Is any example like this?
Is any failure will occur in future?
Pl advise
C.Sabu
Sr.Engineer (Design)
Kochi refineries Ltd.
Cochin
India.
RE: Conversion of VGO (70 Deg C) storage cone tank to 140 Deg C VGO tank.
1. Make sure associated piping can safely handle the expansion due to the higher temperature.
2. Make sure the tank is dry before going above the boiling point of water. When you get the tank in hot service, keep the contents warm enought so that water does not settle out. Otherwise there will be a serious risk of foamover.
HAZOP at www.curryhydrocarbons.ca
RE: Conversion of VGO (70 Deg C) storage cone tank to 140 Deg C VGO tank.
Probably it would be worthwhile to check the TAN values -from naphthenic acidity levels sometimes present in VGOs and acidity that can develop by oxidation with air- and whether these could be corrosive to carbon steel at the new operating conditions. Sludge can form from condensation of oxidation products. If the availability of oxygen is limited by diffusion, there is always the possibility of thermal cleavage of a hydrocarbon chain with the release of hydrogen. Thus, if materials and construction are acceptable at the new conditions, should also consider: inert gas blanketing with breather.