Sorry for such a basic question, but I've looked in the NEC book and can't find the answer, so I'm hoping somebody can point me to the right section that talks about this.
I need to mount a disconnect box on the outside of my house for a 220V/30A run to power a sewer grinder pump.
It would be *very* convenient if the bottom of the box being 2-ft above the ground level would OK according to the NEC code.
I live in NM if that makes any difference.
TIA!
BTW, I'm curious as to what the difference between the IEEE/NEC code (which is what I think I need), and the IEC electrical code because there's a different forum for that.
I need to mount a disconnect box on the outside of my house for a 220V/30A run to power a sewer grinder pump.
It would be *very* convenient if the bottom of the box being 2-ft above the ground level would OK according to the NEC code.
I live in NM if that makes any difference.
TIA!
BTW, I'm curious as to what the difference between the IEEE/NEC code (which is what I think I need), and the IEC electrical code because there's a different forum for that.
RE: 220V Outside disconnect box, height above ground level requirements?
There are exceptions.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 220V Outside disconnect box, height above ground level requirements?
GL
RE: 220V Outside disconnect box, height above ground level requirements?
I can't really ask the code people, NM is one of the stupid states where they won't talk to you, you're supposed to have an electrician do everything or take a trivia test to be able to pull your own permit. The questions are very obscure NEC code questions, nothing about what you really need to know when doing common wiring tasks. It's made so that most people won't bother with it.
RE: 220V Outside disconnect box, height above ground level requirements?
RE: 220V Outside disconnect box, height above ground level requirements?
I'm mostly interested in protecting myself in case the electrician decides to be ornery about my putting in the box for him to wire the rest of the way to the sewage pump. In NM, after all, mere mortals such as myself aren't even supposed to wire a phone from one room to another!
If he complains, I wanted to be ready to be able to quote the electrical code where it says it's OK. I remember it talking about a maximum height someplace, but no minimum height so I was hoping somebody could point me to where it talks about that if it does. Like does the code allow the disconnect to be 6 inches above ground? I wouldn't think so, but I can't find it. But in reality, what I want is for a 2-ft height to be OK.
Thanks!
RE: 220V Outside disconnect box, height above ground level requirements?
"The NEC does not mandate a minimum mounting height for panelboards, disconnects, or meter enclosures. But switches, and circuit breakers used as switches, shall be installed so the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 6 ft 7 in. above the floor or working platform [404.8(A)]. Exception No. 2 permits switches and circuit breakers used as switches to be mounted higher than 6 ft 7 in. if they are located adjacent (next) to the equipment they supply and they are accessible by portable means.
Note: 550.32(F) requires the outdoor mobile home disconnect to be installed so the bottom of the enclosure is not less than 2 ft above finished grade or working platform."
If your electrician becomes ornery - fire him or her. You should just tell him what you want and where you want it. If there is a code conflict, then he or she should
ID the conflict and provide the cite - otherwise, they should get busy and make the install.
GL
RE: 220V Outside disconnect box, height above ground level requirements?
It's more complicated than just firing him. The electrician I'm concerned about will be hired by the town and is contracted for the part between the box on the house and the outside pump. I'm responsible for the part between my service panel and the disconnect box so he has to be willing to connect to my part. When I was in CA, I could do my own wiring and did so. When the inspector came, he asked me who did the wiring because it was such a good job. I know how to do wiring, but I'm not conversant with the myriad of minutia of the code, thus my question.
Thanks!
RE: 220V Outside disconnect box, height above ground level requirements?
However, I still think you should be fine with the 2 ft height - provided there is no other issue such as maintenance clearances, etc.
Good luck
JR
RE: 220V Outside disconnect box, height above ground level requirements?
The situation is a bit odd (some say it's because I'm odd
AFAIK, NM has implemented the NEC code with a few modifications which are more restrictive than the standard code book. But I don't think those extra items affect what I'm doing last time I looked.
RE: 220V Outside disconnect box, height above ground level requirements?
550.32(F), 2017 NEC
You mention though, that this work is being done as part of a town project. They may have their own local regulations and ordinances for how high that disconnect is supposed to be, for when the electrician comes to work on it and finish up the wiring. It's probably stated in a contract (somewhere).
RE: 220V Outside disconnect box, height above ground level requirements?
But in any event, it's now mounted 2 ft, so I hope they'll like it. If not, it can be moved higher and then conduit the wire to the higher location if necessary.
Thanks for all your ideas!
RE: 220V Outside disconnect box, height above ground level requirements?
Thanks
RE: 220V Outside disconnect box, height above ground level requirements?
Thanks for your interest and help, and of course the moral support!
RE: 220V Outside disconnect box, height above ground level requirements?