Water Stopper lost during pouring, what are the options?

Water Stopper lost during pouring, what are the options?

Water Stopper lost during pouring, what are the options?

(OP)


Hi,
Its 20m x 20m water tank, 5.5m height 2200 m3.
After pouring the raft footing something went wrong with the water stopper on one of the sides and it got loose from the footing completely,

What are the possible options for this situation?

Thank You!

RE: Water Stopper lost during pouring, what are the options?

Aside from tearing down the pour, you could pour the rest of the wall, leak test and epoxy inject the leaks.

RE: Water Stopper lost during pouring, what are the options?

How about a coating on the inside? That segregated concrete may leak also.

RE: Water Stopper lost during pouring, what are the options?

You might try hydrotite AND leak test as JedClampett suggested:

http://hydrophilicwaterstops.ca/

RE: Water Stopper lost during pouring, what are the options?

Can you use a vandex coating? One of the reasons I nearly always use a Bentonite 'rod'.

Jed: Might be better to use a polyurethane injection... it's hydrophilic.

Dik

RE: Water Stopper lost during pouring, what are the options?

The hydrophilic and hydrophobic (there's a difference) injection materials definitely have a place in water containing structure design. But the right way to use them is to send divers in with dye wands and to have them inject the injection material from the wet side. My preference is for epoxy, as it provides the structural strength and adhesion to the existing surface to replace the concrete. It's probably not necessary all the time, but I don't want to find out it was the hard way (large noisy cracks, depositions, etc.).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - Addressing Tooling and Casting Requirements at the Design Stage
Several of the tooling and casting requirements of a part can be addressed at the design stage. If these requirements are not addressed at the design stage, lot of time is spent in design iteration when the design reaches the die caster. These design issues lead to increase in time and cost of production leading to delay in time to market and reduced profits for the organization. Download Now
White Paper - The Other Side of Design for Assembly
Assembly level constraints need to be satisfied before the design can move downstream. This white paper will go through the various assembly level issues, which need to be tackled by various organizations on a regular basis. Know more about DFMPro, a design for assembly software. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close