Good day - Any experience with concrete placement at temperatures in the 20F to 40F range without use of heat?  Some manufacturers admixtures are advertised to protect the concrete down to 20F. Ever the skeptics, we are seeking input from unbiased, experienced sources.  Situation is lightweight concrete on metal deck, 16 story building.  Currently using heaters, tarps, and moisture control with apparent, albeit costly, success.  ACI 306 is our bible.  Specifically the question is, have you had success using an accelerating admixture and placing concrete without use of heat at temperatures approaching 20F?  If so, did you implement any other procedures to help ensure success?  And finally, was there any discernible loss of strength evident in the test cylinder breaks?  Thanks in advance for any feedback.

RE: Concrete Placement in Sub Freezing Temperatures

wiff,

it has been my experience that placing concrete in cold weather the key is to let it develop its initial set (500 to 1,000 psi) then it can cool until it freezes with out (too) much damage to the matrix.

Several solutions:

Add an excelerator, to the normal strength concrete.

Increase the strength by 1,000 psi.

Then cover the slab, top and bottom, to conserve the heat the concrete is generating while curing.

Field cured cylinders (cured on site under the blankets on the edge of the slab) will prove if you have been effective.

As an asside, the slower concrete sets the stronger it becomes.  After the initial set, the cold concrete will develope a higher 'ultimate' strength than  concrete that is hot.  That is one reason that cooling pipes were set in the mass concrete placed to form Hoover Dam.

RE: Concrete Placement in Sub Freezing Temperatures

If you are pouring concrete on a metal deck in tempertures below freezing, then I think the method you are currently using is the way to go, expensive, but the best solution.  

Thin sections on metal deck don't generate a lot of heat, at least they don't retain enough when poured on a frozen metal deck.  Warm the deck before the pour, heat the poured slab for 24-48 hours, then let it cool down slowly and move to the next slab.  

That's my two cents.

RE: Concrete Placement in Sub Freezing Temperatures

(OP)
rjeffery & jheidt - Thanks for the input.  In way of feedback, we are staying with the heat and increasing the strength by at least 500 psi.  Concrete is being covered with visqueen for 2-3 days, weather dependent.  The much bigger challenge  turns out to be how to soak the lightweight aggregate in sub freezing temperatures when the plant "doesn't have the capability".  For this we've gone to ACI 304 which permits some water addition on site to account for absorbed moisture.  Ultimately, slump at pump discharge, cylinder breaks, and follow on testing will be the deciding criteria.  Again, thanks. - wiff

RE: Concrete Placement in Sub Freezing Temperatures

rjeffry was right on the money and a better solution.  Insulated tarps on the top and insulation against the underside of the metal decking.  I have poured slabs like this and have had to occasionally let some cool air in.  It will stay warm a minimum of 3 days if insulated properly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - The Evolving Landscape of Commercial Battery-Powered Trucks
What’s driving the evolving landscape of truck electrification? What are the barriers, motivators and strategies for accelerating the electric transition? What insights and resources are available for today’s design engineers working to achieve industry disruption and evolution? For answers to these and other pertinent questions, read this white paper. Download Now
eBook - Rethink Your PLM
A lot has changed since the 90s. You don't surf the Web using dial-up anymore, so why are you still using a legacy PLM solution that's blocking your ability to innovate? To develop and launch products today, you need a flexible, cloud-based PLM, not a solution that's stuck in the past. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close